Com'X210 & IEM3255

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X210 & IEM3255
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
98
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
43
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2025-01-17 04:07 AM

0 Likes
2
191
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-17 04:07 AM

Com'X210 & IEM3255

Please help!

 

I have a Com'X210 (v6.8.7) connected to 16 no. IEM3255 (9600 None) meters but 4 no. of the meters do not return any values when viewed through the Device Settings tab (communication error yellow circle with !).

 

The meters were all added by highlighting the ComX210_F9... (top RH corner of Device Settings tab) and selecting Discover Connected Devices, then labels added and the meters created in the Com'X.

 

When a Check Device Status is run in the Diagnostics tab, all meters have a Status of "In Service".

 

Using Modscan to test the four meters, all values are present and correct.

 

Any thoughts would be appreciated.

 

Thank you 🙂

Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-01-19 09:43 PM

0 Likes
1
158
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-19 09:43 PM

hello @solutions_iems- 

Are they identical ? 

Would it be possible to create a custom model with only one measurement as per modbus table you checked using modscan?

After forcing communication check data do not appear ?

Have you checked the modbus statistics for those devices to check exception codes ?

Kind Regards

See Answer In Context

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2025-02-24 12:47 AM

0 Likes
0
95
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-24 12:47 AM

Hi Guillaume

 

I created a custom model for the IEM3255 using only A/phase, V/phase, P total and real energy and it works OK with the Com'X. My client only needs real energy so everything is now sorted.

 

Thank you!

See Answer In Context

Reply
Replies 2
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-01-19 09:43 PM

0 Likes
1
159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-19 09:43 PM

hello @solutions_iems- 

Are they identical ? 

Would it be possible to create a custom model with only one measurement as per modbus table you checked using modscan?

After forcing communication check data do not appear ?

Have you checked the modbus statistics for those devices to check exception codes ?

Kind Regards

Reply
solutions_iems-
Lt. Commander solutions_iems-
Lt. Commander

Posted: ‎2025-02-24 12:47 AM

0 Likes
0
96
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-02-24 12:47 AM

Hi Guillaume

 

I created a custom model for the IEM3255 using only A/phase, V/phase, P total and real energy and it works OK with the Com'X. My client only needs real energy so everything is now sorted.

 

Thank you!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of