2025-01-1704:07 AM
Com'X210 & IEM3255
Please help!
I have a Com'X210 (v6.8.7) connected to 16 no. IEM3255 (9600 None) meters but 4 no. of the meters do not return any values when viewed through the Device Settings tab (communication error yellow circle with !).
The meters were all added by highlighting the ComX210_F9... (top RH corner of Device Settings tab) and selecting Discover Connected Devices, then labels added and the meters created in the Com'X.
When a Check Device Status is run in the Diagnostics tab, all meters have a Status of "In Service".
Using Modscan to test the four meters, all values are present and correct.