Com'X configuration - adding Panel Server as an ethernet device

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'X configuration - adding Panel Server as an ethernet device
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
swil
Commander swil
Commander

Posted: ‎2022-10-23 03:32 PM

0 Likes
4
1969
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-23 03:32 PM

Com'X configuration - adding Panel Server as an ethernet device

Hi,

Is it possible to add a PAS600 (or PAS800) as a downstream ethernet device in a Com'X 510 / Com'X 210 Configuration?

 

Although the Panel server is not an ethernet device in the Com'X, could the "LINK150" device type be checked to add a Panel Server as a downstream ethernet device. From there would it be possible to add panel server connected serial devices to the Com'X configuration? (where local ID matches  slave id in the Panel server config).

Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2022-10-24 06:46 AM

0 Likes
1
1923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 06:46 AM

The Com'X backend treats all Gateways the same.  The only differences are cosmetic in the UI (Picture and name).  So, you could pick any Gateway in the Com'X to define the Panel Server and it will work.

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 4
Olivier_GARAULT
Lieutenant JG Olivier_GARAULT Lieutenant JG
Lieutenant JG

Posted: ‎2022-10-24 04:10 AM . Last Modified: ‎2022-10-24 04:13 AM

0 Likes
3
1940
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 04:10 AM

Bonjour, 

 

je viens de faire le test en installant un PAS600 entre un PM5111 (SL) et une Com'X510.

Cela fonctionne très bien. 

Il faut déclarer un Link150 dans la Com'X.

Et couper le câble RJ45 sous la Link150 pour le raccordement sur le bornier SL du PAS600...

 

PAS600L LINK150 A.png

PAS600L LINK150 B.png

Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-10-24 05:36 AM

0 Likes
2
1931
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 05:36 AM

Hello,

 

I complete the answer from Olivier by my own test made several month ago (not the last version of Firmware for Panel Server)

 

The Panel Server was defined  in the list of child gateways of  Com'X as a PowerTagLink.

With this definition, the Com' X was able to gather measurments of the Modbus SL products (such as iEM meter)  and SE Wireless products (such as PowerTag)

 

refer to the attached video for demo.

 

BR

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2022-10-24 06:46 AM

0 Likes
1
1924
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 06:46 AM

The Com'X backend treats all Gateways the same.  The only differences are cosmetic in the UI (Picture and name).  So, you could pick any Gateway in the Com'X to define the Panel Server and it will work.

Tags (1)
  • Tags:
  • english
Reply
swil
Commander swil
Commander

Posted: ‎2022-10-24 07:39 PM

0 Likes
0
1905
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 07:39 PM

Thanks for the replies everyone. 

 

It's good to have that answered.

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore