PAS600L - Time to Refresh - IEM3155

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS600L - Time to Refresh - IEM3155
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Kevin08
Kevin08 Cadet
Cadet

Posted: ‎2022-10-24 06:34 AM

0 Likes
2
953
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 06:34 AM

PAS600L - Time to Refresh - IEM3155

Hello Community !

 

I'm working on a project which embeded PAS600L device & I need help.

 

I'm looking to know the minimum time periode (in sec) we can ask to the PAS600L for energy consumption measured by 22x IEM3155 linked in DaisyChain ?

We're looking for less than 2s.

 

 

Thanks in advance,

 

Kevin

Labels
  • Labels:
  • Product selection
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-10-24 09:45 AM

0 Likes
1
927
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 09:45 AM

Hello Kevin,

 

My understanding is that you want to collect the 22 meters in a time interval of 2 seconds.

It means that the average time will be 2s/22=90 ms to request each meter so  it is a demanding architecture very close  to the maximum performance of a modbus SL fieldbus ! (or too high...?) 

It depends of the Panel Server of course but also of the response time of the iem meters themselves.

So not possible to definitively answer to your question without test on the architecture !

 

Some advises:

  - find the "just enough" inter frame delay in the PAS 600 parameters (default settings on PAS=10 ms but depending of the performance of the downstream products, this time must be sometime increased up to 50ms or more )

  -  Upper modbus TCP client must request each meter ONLY for the energy modbus registers (and not for other registers!)

  -  use the Panel Server as a transparent gateway without discovery of the iemmeter in the Panel Server web page . the discovery in Panel server generates an additional and periodic traffic to check if the downstream products are still connected

(use the discovery feature when you commission your installation to check that iemmeters are reachable ... but delete it in the Panel Server before  connection of  the upper modbus TCP client)

  -  keep in mind that the disconnection of one iem meter, will generate time out issues with impact on the polling of the whole installation

 

One question: typical collecting time interval for energy monitoring is X minutes. What is your use case ? is it for  control ? / load shedding ? other?

 

BR  

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Tun
Ensign Tun Ensign
Ensign

Posted: ‎2022-10-24 08:07 PM

0 Likes
0
916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 08:07 PM

Thanks for your inputs @Thierry_Baudard .

 

Not sure it is relevant to ask PME's "Daisy-Chain Calculator" in this forum?

How does PME's Daisy-Chain Calculator defines a specific response time (e.g 2 sec) that we are discussing here?

As far as I understand, it does only defines the maximum number of downstream devices in a single daisy-chain. 

 

Best Regards

Tun

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now