Hi, I'm trying to connect a PAS600 device to PME server via Wi-Fi (Internal Antenna ,DHCP mode ).
We have successfully established connection and can browse the webpage ,but unable to read the data through modscan or PME management console.
Any procedures must be followed when joining through DHCP mode ?
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Hello,
1) Check that you use the last Panel Server fw version 1.4.0
2) Remove all the Ethernet cable of the PAS and confirm that you can navigate in Panel Server web page (but according to your post it should be OK)
3)Click the modbus case in Setting>Newtork Communication >Services (screenshot in attachment) then redo the test.
Can you please confirm in the forum if it solves (or not!) your problem.