I i Remote access to PAS600

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • I i Remote access to PAS600
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
igor_iskakov
Ensign igor_iskakov Ensign
Ensign

Posted: ‎2022-10-10 10:58 PM

1 Like
6
5746
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-10 10:58 PM

I i Remote access to PAS600

Hi is it possible have first access to PAS via open Ethernet just setting forward port to PAS.

Or first access must be always directly to PAS

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-10-11 03:26 AM

1 Like
1
5716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-11 03:26 AM

Hi @igor_iskakov , 

 

What is the FW version of your Panel Server ? You may have some difficulties if you are in 001.002.000.


We have a customer using port forwarding on a Sierra 4G router + external provider to have a public IP through a Proxy and this is working well with 001.003.002 and higher. Customer can access the data on its EV charging station through the PAS600. 

 

4G router is forwarding port 443 of the Panel Server to port 8319 (can be changed on the router interface).

 

Question: what is a CS demand ?

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
igor_iskakov
Ensign igor_iskakov Ensign
Ensign

Posted: ‎2022-10-11 03:29 AM

0 Likes
0
5714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-11 03:29 AM

Thanks, will check

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-10-11 02:07 AM

1 Like
5
5728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-11 02:07 AM

Hello Igor,

 

Default in factory settings, for both gateway types (PAS 600 and PAS800) are:

- both ports are in switched mode (same IP address for both ports)

- the method of assigning the IP V4 address is DHCP

- the method of assigning the IP V4 address of the gateway is DHCP

- the IPV6 address is activated

- the proxy is inactive

 

Connecting to an Ethernet network:

Obviously, if you connect the Panel Server to an Ethernet infrastructure that includes a DHCP server to provide Ethernet parameters and no other IT rules to block Panel Server traffic, an Ethernet client such as a laptop computer connected to that network may to access the Panel Server (using IPV4 addresses previously assigned by the DHCP server.)

 

However, keep in mind that it depends not only on the Panel Server but also on the IT rules (firewalls...) inside the Ethernet infrastructure.

 

Direct connection:

We recommend this mode especially for users who are not familiar with Ethernet network administration. Refer to user guide ref A0172EN-xx  § getting started with EcoStrxure Panel Server web page (I also add a pdf extract of this § in attachment)

 

BR

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Attachments
Tags (1)
  • Tags:
  • english
Reply
igor_iskakov
Ensign igor_iskakov Ensign
Ensign

Posted: ‎2022-10-11 02:57 AM

0 Likes
4
5719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-11 02:57 AM

I have setup the PAS with correct local IP, access to the internet and new password for the SecurityAdmin user. 

 

Then went on the router to forward a port (external) to the local IP of the PAS. When I try to log on externally it won’t work because there is a CS demand that it not be exposed on the internet directly. 

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-10-11 03:26 AM

1 Like
1
5717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-11 03:26 AM

Hi @igor_iskakov , 

 

What is the FW version of your Panel Server ? You may have some difficulties if you are in 001.002.000.


We have a customer using port forwarding on a Sierra 4G router + external provider to have a public IP through a Proxy and this is working well with 001.003.002 and higher. Customer can access the data on its EV charging station through the PAS600. 

 

4G router is forwarding port 443 of the Panel Server to port 8319 (can be changed on the router interface).

 

Question: what is a CS demand ?

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
igor_iskakov
Ensign igor_iskakov Ensign
Ensign

Posted: ‎2022-10-11 03:29 AM

0 Likes
0
5715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-11 03:29 AM

Thanks, will check

Tags (1)
  • Tags:
  • english
Reply
igor_iskakov
Ensign igor_iskakov Ensign
Ensign

Posted: ‎2022-10-12 04:12 AM

0 Likes
1
5687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-12 04:12 AM

Thank you issue is solved after FW update.

Tags (1)
  • Tags:
  • english
Reply
ELKINDI-ZMT
Ensign ELKINDI-ZMT
Ensign

Posted: ‎2022-10-26 01:51 PM

0 Likes
0
5515
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-26 01:51 PM

Hello @igor_iskakov 

 

I would like to perform PAS link to the PAS600 can you please share your eperience (my pas is AZURE , what is yours ?

 

Thanks 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore