Device type - IFM Module for Breakers - Com'X and Panel Server

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Device type - IFM Module for Breakers - Com'X and Panel Server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
swil
Commander swil
Commander

Posted: ‎2022-10-23 06:42 PM

0 Likes
2
1431
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-23 06:42 PM

Device type - IFM Module for Breakers - Com'X and Panel Server

Looking at https://www.se.com/ww/en/faqs/FA285178/

, it appears that there is several types of IFM devices for similarly named breaker models. 

 

Regarding device type selection in Schneider gateways (Com'X / PAS server):

 

1. In a Com'X, Is a Compact NS is an A/E/H/P com'x model type selected for NSX breakers with Micrologic A/E/H/P trip units?

2. Is there a similar file to the above link detailing supported devices for Ecostruxure Panel Servers (e.g. PAS600 / PAS800)? If so, please provide it.

 

Thanks

 

 

Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-10-24 12:02 AM

0 Likes
1
1406
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 12:02 AM

Hello @swil , 

 

FA285178 is not up to date. Better look at the matrix file delivered with the Com'X FW package.

Compact NS has not the same Trip Units as Compact NSX.

If you integrate a Compact NSX please select:

  • Compact NSX A IFE or Compact NSX E IFE if connected through Ethernet
  • Compact NSX A or E if connected through Modbus Serial

 

Compact NS is sharing the same Micrologic trip units as MasterPact. Try to declare your Compact NS as Masterpact A/P/E/H device type.

Capture d’écran 2022-10-24 085844.jpg

 

Capture d’écran 2022-10-24 085844.jpg

 

For the Panel Server, the list of compatible devices is described on the release notes:

https://www.productinfo.schneider-electric.com/ecostruxurepanelserverrn/doca0178-ecostruxure-panel-s...

Regards, 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-10-24 01:01 AM

0 Likes
0
1403
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-10-24 01:01 AM

Hello swill


As you mention in your post, there are two generation of IFM gateway (gen1: TRV00210 and gen2: LV434000)

 

hereunder the answer to the Question2 of your post about compatibility of IFM with Panel Server.

 

Even if the  two generation of IFM  are supported by the Panel Server , You must check that the association of IFM+ the downstream circuit breaker is supported (not only the IFM interface!)

To do this, please refer to the the release note of the Panel Server (PAS600 : ref DOCA0178EN-05 / PAS800: ref DOCA0248EN-02) § Supported devices/Modbus serial Devices

Note also that  release note are updated for each new fw version... so  take care to use the last one

 

BR 

 

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore