Hi,
Is it possible to add a PAS600 (or PAS800) as a downstream ethernet device in a Com'X 510 / Com'X 210 Configuration?
Although the Panel server is not an ethernet device in the Com'X, could the "LINK150" device type be checked to add a Panel Server as a downstream ethernet device. From there would it be possible to add panel server connected serial devices to the Com'X configuration? (where local ID matches slave id in the Panel server config).
Link copied. Please paste this link to share this article on your social media post.
The Com'X backend treats all Gateways the same. The only differences are cosmetic in the UI (Picture and name). So, you could pick any Gateway in the Com'X to define the Panel Server and it will work.
Link copied. Please paste this link to share this article on your social media post.
Bonjour,
je viens de faire le test en installant un PAS600 entre un PM5111 (SL) et une Com'X510.
Cela fonctionne très bien.
Il faut déclarer un Link150 dans la Com'X.
Et couper le câble RJ45 sous la Link150 pour le raccordement sur le bornier SL du PAS600...
Link copied. Please paste this link to share this article on your social media post.
Hello,
I complete the answer from Olivier by my own test made several month ago (not the last version of Firmware for Panel Server)
The Panel Server was defined in the list of child gateways of Com'X as a PowerTagLink.
With this definition, the Com' X was able to gather measurments of the Modbus SL products (such as iEM meter) and SE Wireless products (such as PowerTag)
refer to the attached video for demo.
BR
Link copied. Please paste this link to share this article on your social media post.
The Com'X backend treats all Gateways the same. The only differences are cosmetic in the UI (Picture and name). So, you could pick any Gateway in the Com'X to define the Panel Server and it will work.
Link copied. Please paste this link to share this article on your social media post.
Thanks for the replies everyone.
It's good to have that answered.