Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
30 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
A client is requesting a metering system for many production lines (~70) and they want the metering system to include the calculaton of equivalent Co2 tons. They're looking for a system as cheap as possible, so PME is not in the scope of the project. Is there a way to calculate these values directly in the ComX 510 and report them back to the client?
Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hello @Nedjma ,
@p_dejarmy_encos asked a similar question for Power Meters here :https://community.se.com/t5/Power-Metering/Co2-calculations-in-energy-meter/m-p/187756#M3833
Com'X510 can perform data logging but not data aggregation. Com'X is not able to perform any calculation.
So the Com'X cannot fit the need.
Regards,
Romain
Posted: 2020-02-06 02:12 AM
Link copied. Please paste this link to share this article on your social media post.
Hi the community members can you help this member on this topic please?
@Romain_Polette do you think you can advise on this topic?
@p_dejarmy_encos if you still in the same situation please do not hesitate to inform us here.
Link copied. Please paste this link to share this article on your social media post.
Hello @Nedjma ,
@p_dejarmy_encos asked a similar question for Power Meters here :https://community.se.com/t5/Power-Metering/Co2-calculations-in-energy-meter/m-p/187756#M3833
Com'X510 can perform data logging but not data aggregation. Com'X is not able to perform any calculation.
So the Com'X cannot fit the need.
Regards,
Romain
Posted: 2020-02-06 05:41 AM . Last Modified: 2022-10-19 02:33 AM
Link copied. Please paste this link to share this article on your social media post.
Hello @Romain_Polette,
Thank you for informing me about this double topic.
@p_dejarmy_encos as you have already posted here and you have got your problem solved I allow myself to close this topic. Indeed the guidelines of the community (check here) not allow to publish the same questions in different areas.
I kindly invite all the community members to click on this link to have the answer for this question : https://community.se.com/t5/Power-Metering/Co2-calculations-in-energy-meter/m-p/187756#M3833
Thank you for your understanding!
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.