Com'x510 is SMTP connected but fails to send an Email

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Com'x510 is SMTP connected but fails to send an Email
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-01-30 02:25 AM

0 Likes
4
1187
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-30 02:25 AM

Com'x510 is SMTP connected but fails to send an Email

Hi Guys,

We set up the com'X510 in a facility.

 

The network topology of the project is there is as mentioned:

* A centrally managed switch for all of our devices

* Each device is connected with its own ethernet cable

* From the switch, there is an ethernet cable that goes to a router that has internet access and provides the internet to all of the devices.

 

We entered the SMTP server details to the Com'X 510 as explained.

We know for a fact that the email settings are correct since we have a SpaceLynk on-premise using the same SMTP settings,
from it, we send emails with no issue.

 

We tried configuring the 2 ethernet ports to a "2 separate IP" setting and got an Error that emails can't be sent (SMTP error). since apparently the publishing requires another ethernet cable for sending in port 2 (WAN), which we didn't have.

 

We tried configuring the 2 ethernet ports to "1 address for both" setting so that publishing and managing are through the same port.

This is our preferred method since there is only 1 cable coming from the switch.

 After these settings were applied, we couldn't access the ComX anymore through both ports and had to factory reset the unit.

 

Please advise,

 

@Anonymous user @Anonymous user 

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-02-07 02:22 AM

0 Likes
0
1167
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-07 02:22 AM

Hi @Anonymous user,

 

Did you find your answer to the replies above?

If yes, please click on "Accept as Solution" at the bottom right corner of the answer which helps you.

So other members can find the same solution through the search bar.

 

Thank you!

See Answer In Context

Reply
Replies 4
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-01-30 06:56 AM

0 Likes
2
1181
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-30 06:56 AM

Hello @Anonymous user , 

 

What is the FW version of your Com'X and what is your e-mail provider ?

 

This issue can be related to a "trust" between the Certificates (cipher suites) included in the Com'X and the SMTP Server of your e-mail provider.

 

Regards, 

 

Romain

Romain POLETTE
Solution Architect - France Operations
Reply
Anonymous user
Not applicable

Posted: ‎2020-02-03 01:01 AM

0 Likes
1
1176
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-03 01:01 AM

Hi Romain
Our Com'x510 Version is 6.5.4
and the E-mail provider: we tried SMTP services from AOL, Google's Gsuite and Walla. all the same results.
The fact that the SpaceLynk unit on-site sends emails perfectly with all of these same providers suggests that the problem is not in the SMTP Provider but some setting on the Com'x510

Reply
james-wood-tel
Crewman james-wood-tel Crewman
Crewman

Posted: ‎2020-02-03 03:46 AM

0 Likes
0
1174
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-03 03:46 AM

Hi, have you tried using the app password generation in Gmail Security settings. It's a way of approving a hardware item for mailing out.

 

Email Server Information Generation

 

Create a new google account.

 

Click on your Manage your Google Account

 

Click on Security

 

Click on App Passwords. Enter your Account Password

 

Select Mail and Other (Custom Name) form the drop down and then add a name for the device you want to email out from. Click Generate

 

Take a note or copy the new password generated into the email server settings for your ComX.

 

Hope that helps

Reply
Anonymous user
Not applicable

Posted: ‎2020-02-07 02:22 AM

0 Likes
0
1168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-02-07 02:22 AM

Hi @Anonymous user,

 

Did you find your answer to the replies above?

If yes, please click on "Accept as Solution" at the bottom right corner of the answer which helps you.

So other members can find the same solution through the search bar.

 

Thank you!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore