Berapakah maximum Drop Voltage pada instalasi listrik?

Expert on Demand for Standards & Regulations

Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Power Distribution IEC
  • Expert on Demand for Standards & Regulations
  • Berapakah maximum Drop Voltage pada instalasi listrik?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
HelvinHermanT
Admiral HelvinHermanT Admiral
106
faisalamir
Lieutenant faisalamir Lieutenant
7
Dwinanto_Setyadi
Lieutenant JG Dwinanto_Setyadi Lieutenant JG
7
VickyTanzil
Ensign VickyTanzil Ensign
5
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Expert on Demand for Standards & Regulations
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2021-11-03 12:17 AM

0 Likes
4
6404
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 12:17 AM

Berapakah maximum Drop Voltage pada instalasi listrik?

Siang, mau tanya, maximum Drop Voltage pada instalasi listrik itu berapa ya? Terima kasih.

Labels
  • Labels:
  • Indonesia
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-03 07:27 PM . Last Modified: ‎2021-11-03 07:28 PM

1 Like
3
6398
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 07:27 PM . Last Modified: ‎2021-11-03 07:28 PM

Selamat Siang juga,

 

Terima kasih atas pertanyaannya.

 

Rekomendasi maximum Drop Voltage dalam instalasi diatur dalam IEC 60364-5-52:2009 Low-voltage electrical installations – Part 5-52: Selection and erection of electrical equipment – Wiring systems

 

Bisa dilihat dalam Annex / Lampiran G mengenai "Volrtage drop in customers installations". Nilai maximum drop voltage adalah 3 - 8 % tergantung tipe instalasinya dan peruntukannya (Penerangan atau lain lain). 

 

Contoh :

Maximum drop voltage sebesar 3% untuk Penerangan (Lighting) jika disuplai dari Distribusi Listrik Umum tegangan rendah (PLN) dan maximum 6% untuk penerangan dengan suplai dari distribusi listrik tegangan rendah Privat.

Untuk penggunaan lainnya (selain penerangan) maximum drop voltage 5-8% untuk Distribusi Umum dan Private.

 

Dimungkinkan drop voltage lebih besar saat starting motor atau gawai dengan inrush current besar.

 

Voltage Drop Formula.jpg

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-04 10:08 PM . Last Modified: ‎2021-11-04 10:09 PM

In response to Anonymous user
0 Likes
1
6382
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-04 10:08 PM . Last Modified: ‎2021-11-04 10:09 PM

 

u is the voltage drop in volts;
b is the coefficient equal to 1 for three-phases circuits, and equal to 2 for single-phasecircuits;


NOTE 3 Three-phase circuits with the neutral completely unbalanced (a single phase loaded) are considered a single-phase circuits.


ρ1 is the resistivity of conductors in normal service, taken equal to the resistivity at the temperature in normal service, i.e. 1,25 times the resistivity at 20 °C, or 0, 022 5 Ωmm2/m for copper and 0,036 Ωmm2/m for aluminium;


L is the straight length of the wiring systems, in metres;

 

S is the cross-sectional area of conductors, in mm2;


cos ϕ is the power factor; in the absence of precise details, the power factor is taken as equal to 0,8 (sin ϕ = 0,6);


λ is the reactance per unit length of conductors, which is taken to be 0,08 mΩ/m in the absence of other details;


IB is the design current (in amps);

 

Lebih lengkapnya bisa dilihat di standar tersebut. 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-03 07:27 PM . Last Modified: ‎2021-11-03 07:28 PM

1 Like
3
6399
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-03 07:27 PM . Last Modified: ‎2021-11-03 07:28 PM

Selamat Siang juga,

 

Terima kasih atas pertanyaannya.

 

Rekomendasi maximum Drop Voltage dalam instalasi diatur dalam IEC 60364-5-52:2009 Low-voltage electrical installations – Part 5-52: Selection and erection of electrical equipment – Wiring systems

 

Bisa dilihat dalam Annex / Lampiran G mengenai "Volrtage drop in customers installations". Nilai maximum drop voltage adalah 3 - 8 % tergantung tipe instalasinya dan peruntukannya (Penerangan atau lain lain). 

 

Contoh :

Maximum drop voltage sebesar 3% untuk Penerangan (Lighting) jika disuplai dari Distribusi Listrik Umum tegangan rendah (PLN) dan maximum 6% untuk penerangan dengan suplai dari distribusi listrik tegangan rendah Privat.

Untuk penggunaan lainnya (selain penerangan) maximum drop voltage 5-8% untuk Distribusi Umum dan Private.

 

Dimungkinkan drop voltage lebih besar saat starting motor atau gawai dengan inrush current besar.

 

Voltage Drop Formula.jpg

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-04 09:33 PM

In response to HelvinHermanT
0 Likes
2
6388
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-04 09:33 PM

Terima kasih atas informasinya, Pak @HelvinHermanT !

Untuk rumus di atas, mohon maaf ada legend lengkapnya ngga ya Pak? Seperti S, lamda, Ib, maksudnya apa, Karena terpotong.

 

Terima kasih!

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

HelvinHermanT
Admiral HelvinHermanT Admiral
Admiral

Posted: ‎2021-11-04 10:08 PM . Last Modified: ‎2021-11-04 10:09 PM

In response to Anonymous user
0 Likes
1
6383
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-04 10:08 PM . Last Modified: ‎2021-11-04 10:09 PM

 

u is the voltage drop in volts;
b is the coefficient equal to 1 for three-phases circuits, and equal to 2 for single-phasecircuits;


NOTE 3 Three-phase circuits with the neutral completely unbalanced (a single phase loaded) are considered a single-phase circuits.


ρ1 is the resistivity of conductors in normal service, taken equal to the resistivity at the temperature in normal service, i.e. 1,25 times the resistivity at 20 °C, or 0, 022 5 Ωmm2/m for copper and 0,036 Ωmm2/m for aluminium;


L is the straight length of the wiring systems, in metres;

 

S is the cross-sectional area of conductors, in mm2;


cos ϕ is the power factor; in the absence of precise details, the power factor is taken as equal to 0,8 (sin ϕ = 0,6);


λ is the reactance per unit length of conductors, which is taken to be 0,08 mΩ/m in the absence of other details;


IB is the design current (in amps);

 

Lebih lengkapnya bisa dilihat di standar tersebut. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-11-07 07:39 PM

In response to HelvinHermanT
1 Like
0
6375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-11-07 07:39 PM

Siap, terima kasih informasinya Pak @HelvinHermanT !

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore