Ask our Experts
Didn't find what you are looking for? Ask our experts!
New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Connect to Schneider Electric experts in your country for any inquiry about electrical installation and safety standards and regulations.
Search in
Please select a country to continue with beta search.
Posted: 2021-11-03 12:17 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-03 07:27 PM . Last Modified: 2021-11-03 07:28 PM
Selamat Siang juga,
Terima kasih atas pertanyaannya.
Rekomendasi maximum Drop Voltage dalam instalasi diatur dalam IEC 60364-5-52:2009 Low-voltage electrical installations – Part 5-52: Selection and erection of electrical equipment – Wiring systems
Bisa dilihat dalam Annex / Lampiran G mengenai "Volrtage drop in customers installations". Nilai maximum drop voltage adalah 3 - 8 % tergantung tipe instalasinya dan peruntukannya (Penerangan atau lain lain).
Contoh :
Maximum drop voltage sebesar 3% untuk Penerangan (Lighting) jika disuplai dari Distribusi Listrik Umum tegangan rendah (PLN) dan maximum 6% untuk penerangan dengan suplai dari distribusi listrik tegangan rendah Privat.
Untuk penggunaan lainnya (selain penerangan) maximum drop voltage 5-8% untuk Distribusi Umum dan Private.
Dimungkinkan drop voltage lebih besar saat starting motor atau gawai dengan inrush current besar.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-04 10:08 PM . Last Modified: 2021-11-04 10:09 PM
u is the voltage drop in volts;
b is the coefficient equal to 1 for three-phases circuits, and equal to 2 for single-phasecircuits;
NOTE 3 Three-phase circuits with the neutral completely unbalanced (a single phase loaded) are considered a single-phase circuits.
ρ1 is the resistivity of conductors in normal service, taken equal to the resistivity at the temperature in normal service, i.e. 1,25 times the resistivity at 20 °C, or 0, 022 5 Ωmm2/m for copper and 0,036 Ωmm2/m for aluminium;
L is the straight length of the wiring systems, in metres;
S is the cross-sectional area of conductors, in mm2;
cos ϕ is the power factor; in the absence of precise details, the power factor is taken as equal to 0,8 (sin ϕ = 0,6);
λ is the reactance per unit length of conductors, which is taken to be 0,08 mΩ/m in the absence of other details;
IB is the design current (in amps);
Lebih lengkapnya bisa dilihat di standar tersebut.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-03 07:27 PM . Last Modified: 2021-11-03 07:28 PM
Selamat Siang juga,
Terima kasih atas pertanyaannya.
Rekomendasi maximum Drop Voltage dalam instalasi diatur dalam IEC 60364-5-52:2009 Low-voltage electrical installations – Part 5-52: Selection and erection of electrical equipment – Wiring systems
Bisa dilihat dalam Annex / Lampiran G mengenai "Volrtage drop in customers installations". Nilai maximum drop voltage adalah 3 - 8 % tergantung tipe instalasinya dan peruntukannya (Penerangan atau lain lain).
Contoh :
Maximum drop voltage sebesar 3% untuk Penerangan (Lighting) jika disuplai dari Distribusi Listrik Umum tegangan rendah (PLN) dan maximum 6% untuk penerangan dengan suplai dari distribusi listrik tegangan rendah Privat.
Untuk penggunaan lainnya (selain penerangan) maximum drop voltage 5-8% untuk Distribusi Umum dan Private.
Dimungkinkan drop voltage lebih besar saat starting motor atau gawai dengan inrush current besar.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-04 09:33 PM
Terima kasih atas informasinya, Pak @HelvinHermanT !
Untuk rumus di atas, mohon maaf ada legend lengkapnya ngga ya Pak? Seperti S, lamda, Ib, maksudnya apa, Karena terpotong.
Terima kasih!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-11-04 10:08 PM . Last Modified: 2021-11-04 10:09 PM
u is the voltage drop in volts;
b is the coefficient equal to 1 for three-phases circuits, and equal to 2 for single-phasecircuits;
NOTE 3 Three-phase circuits with the neutral completely unbalanced (a single phase loaded) are considered a single-phase circuits.
ρ1 is the resistivity of conductors in normal service, taken equal to the resistivity at the temperature in normal service, i.e. 1,25 times the resistivity at 20 °C, or 0, 022 5 Ωmm2/m for copper and 0,036 Ωmm2/m for aluminium;
L is the straight length of the wiring systems, in metres;
S is the cross-sectional area of conductors, in mm2;
cos ϕ is the power factor; in the absence of precise details, the power factor is taken as equal to 0,8 (sin ϕ = 0,6);
λ is the reactance per unit length of conductors, which is taken to be 0,08 mΩ/m in the absence of other details;
IB is the design current (in amps);
Lebih lengkapnya bisa dilihat di standar tersebut.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.