EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:12 PM
(CID:123997485)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:12 PM
Hi Dolencio,
Please specify what appliance you are connecting the sensor pod 150 to, and also what sensors you will be connecting to the sensor pod 150.
Thanks
(CID:123997525)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:12 PM
Hi Dolencio,
Please specify what appliance you are connecting the sensor pod 150 to, and also what sensors you will be connecting to the sensor pod 150.
Thanks
(CID:123997525)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:12 PM
See FAQ FA156087 for the maximum cable lengths between the sensor pod 150 and the various sensors. If you exceed these lengths, the sensors will likely report as unplugged or N/A, so you wont get any readings from them. Also, you may need to use repeaters if the distance between the appliance and the sensor pod 150 is greater than 100 meters.
(CID:123997535)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:11 PM
Hi Thompson, i am using Netbotz570 to connect the Pode150. and Sometimes . i am conneting a contact Dry (Levato BG091A) I have to contact dry with same brand and are all NO. i am controlling Power issue. but one of them sometimes loses the configuration.
(CID:123997545)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:11 PM
Hi Thompson, i am using Netbotz570 to connect the Pode150. and Sometimes . i am conneting a contact Dry (Levato BG091A) I have to contact dry with same brand and are all NO. i am controlling Power issue. but one of them sometimes loses the configuration.
(CID:123997727)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:11 PM
Are you also using the NBES0304 dry contact cable to connect to the Levato device?
If you are, the cable should not be more than 30.5 meters or 100 feet. If the cable is within that length, then you should probably contact your local Technical Support to troubleshoot the issue you are having.
(CID:123997725)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:11 PM
you said before that i can use repeater to extend the cable. can you please specify the repeater refence. yes i am usings NBES0304 dry contact Cable the has 4 cable 1 black, 1 red and 2 green Cable.
(CID:123997721)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:07 PM . Last Modified: β2024-04-07 11:11 PM
you said before that i can use repeater to extend the cable. can you please specify the repeater reference that i can find. yes i am using NBES0304 dry contact Cable the has 4 cable 1 black, 1 red and 2 green Cable.
(CID:123997691)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
The repeaters could only be used for the A-Link communication between the 570 and the sensor pod 150. You cannot use them anywhere else.
(CID:123997717)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
that means that i can move the pod for some where near the Levato devise and save the length of the cable. so my question is what is the recommended length between the pod 150 and the 570.
(CID:123997713)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
The length of the cable between the 570 and sensor pod 150 can be up to 1000 meters, but you would need to use a repeater after every 100 meters.
If the distance between your 570 and pod 150 is less than 100 meters, then you can just use the one cable.
Hope this is clear.
(CID:123997709)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
Thanks John. Now i Know how to troubleshooting and resolve the issue.
(CID:123997705)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
other Question Thompson i need to be clarified is:
1.can i use an Normal APC Sensor to attach on the Sensor pod150 or the pod is only used for third Part Sensor.?
2. how can or is it Possible to add more cameras on my 570 as it only has 4 USB PORT_?
(CID:123997620)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
other Question Thompson i need to be clarified is:
1.can i use an Normal APC Sensor to attach on the Sensor pod150 or the pod is only used for third Part Sensor.?
2. how can or is it Possible to add more cameras on my 570 as it only has 4 USB PORT_?
(CID:123997693)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
(CID:123997697)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2024-04-07 11:11 PM
(CID:124520971)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:08 PM . Last Modified: β2023-10-22 09:38 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.