rsyslog for ITA 932

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Re: rsyslog for ITA 932
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
63
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
RomeoEtisJr
Ensign RomeoEtisJr Ensign
Ensign

Posted: ‎2023-01-30 11:43 PM

0 Likes
2
1249
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-30 11:43 PM

rsyslog for ITA 932

Hi Team,

 

One of our VIP customer requires their ITA server to send server logs to a remote server.

Does ITA support this? may we know the procedure? Today they did tried to configure rsyslogs but the file sent is 0.

 

 

In the console do we need to enable #forwardtosyslog which is currently showing NO?

ITA Console .jpg

rsyslog file sent by ITA is 0

 

Syslog result.jpg

 

Thanks,

 

Romeo

Labels
  • Labels:
  • IT Advisor
  • Tags:
  • english
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
gsterling
Captain gsterling Captain
Captain

Posted: ‎2023-01-31 06:45 AM

1 Like
1
1212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 06:45 AM

Hello Romeo

 

It should be possible to configure the ITA server to forward messages to a rsyslog server or a system like splunk.

 

A change has been made to recent ITA releases which makes this process easier, but for ITA 9.3.2 check these steps to setup the forwarding.

 

Schneider installs a file in /etc/rsyslog.d named “operation-logs.conf”.

 

  • You will need to edit the operation-logs.conf file, and comment the three lines containing the word “stop” by placing a “#” character on those lines before the word “stop”.
  • Save the changes to the file.

The above change is no longer required in newer ITA releases (9.3.5 and newer I think).

 

After making the above changes, you can use this process to forward log messages remotely.

 

Edit /etc/rsyslog.conf.

 

Add the forwarding directive in this format. You should be able to place this line at the bottom of the rsyslog.conf file. The below statement forwards all log messages.

*.* @@<remote-server>:<remote-port>

 

Then restart the rsyslog service

systemctl restart rsyslog

 

Regards

 

Greg Sterling

See Answer In Context

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Replies 2
gsterling
Captain gsterling Captain
Captain

Posted: ‎2023-01-31 06:45 AM

1 Like
1
1213
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-01-31 06:45 AM

Hello Romeo

 

It should be possible to configure the ITA server to forward messages to a rsyslog server or a system like splunk.

 

A change has been made to recent ITA releases which makes this process easier, but for ITA 9.3.2 check these steps to setup the forwarding.

 

Schneider installs a file in /etc/rsyslog.d named “operation-logs.conf”.

 

  • You will need to edit the operation-logs.conf file, and comment the three lines containing the word “stop” by placing a “#” character on those lines before the word “stop”.
  • Save the changes to the file.

The above change is no longer required in newer ITA releases (9.3.5 and newer I think).

 

After making the above changes, you can use this process to forward log messages remotely.

 

Edit /etc/rsyslog.conf.

 

Add the forwarding directive in this format. You should be able to place this line at the bottom of the rsyslog.conf file. The below statement forwards all log messages.

*.* @@<remote-server>:<remote-port>

 

Then restart the rsyslog service

systemctl restart rsyslog

 

Regards

 

Greg Sterling

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

RomeoEtisJr
Ensign RomeoEtisJr Ensign
Ensign

Posted: ‎2023-02-02 12:54 AM

In response to gsterling
0 Likes
0
1204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-02-02 12:54 AM

Thanks Greg!

 

This works for me. 

 

Romeo

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of