"Critical Communication error with device"

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase β†’ Use quotes " " (e.g., "error 404")
  • Wildcard β†’ Use * for partial words (e.g., build*, *tion)
  • AND / OR β†’ Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short β†’ Use 2–3 relevant words , not full sentences
  • Filters β†’ Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • "Critical Communication error with device"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

0 Likes
8
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

"Critical Communication error with device"

(CID:126880871)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

0 Likes
6
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

Hi Michael,

 

I'm not sure if you omitted the extra information for your post but the only thing that came across was the subject: "Critical Communication error with device".

I'm assuming you're having issues between DCE and a NetBotz device as DCE and NetBotz were provided as as products.

Please provide a little more detail.

What NetBotz appliance are you using? What version DCE? What version of Botzware?

Is this a permanent issue or intermittent?

Logs from both DCE and the appliance would be helpful. 

Is this a single device having this issue or multiple devices?

If multiple devices, do they all exhibit this issue at the same time?

If a single device, what is it's configuration?

Is the device plugged into a UPS?

Is the device using SNMP? which version?

If NetBotz 3xx, 4xx, or 5xx, is it set to http or https?

 

Basic info like this would be helpful in starting to diagnose the issue.

 

Thanks,

Steve

 

(CID:126880879)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

In response to DCIM_Support
0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

Hi Steve,

Sorry about that.  I didn't intend to post a question, but now that I have...  I'm trying to find out how these emails are being generated.  I'm assuming that they are coming via DCE (Version 7.3.1.114).  The IPs that the emails list are NetBotz devices (Version 4.5.2.20160602.1247). 

I believe that I need to modify the distribution list.

Here is an example of the emails that were sent out:

 

--------------------  Start of email   --------------

 

 

-----Original Message-----
From: DCE@yyc.com [mailto:DCE@yyc.com]
Sent: December-12-17 2:03 AM

Subject: Critical Communication error with device 172.21.1.56

 

-- Report from MGMT-DCIM01.mgmt.yyc.com_(10.1.0.49) at http://MGMT-DCIM01.mgmt.yyc.com, at 12/12/17 02:02 AM --

 

Device is online

 

---------------------  End of email   ---------------------

 

Any assistance you can provide is appreciated.

 

Thanks again,

 

Michael Adachi

(CID:126880907)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

In response to DCIM_Support
0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

Hi Michael,

Gotcha. It happens often, you try searching posts and it ends up being a post itself. I've done it myself. 

Basically any event on the NetBotz itself (3xx, 4xx, and 5xx) causes the device itself to alarm. When the appliance loses communications with DCE however, DCE does send these e-mails noting the loss of communications. 

Any user in the system, local, LDAP, or Active Directory, that has an e-mail address associated with the user name AND that has the ability to view that device should receive the lost comm e-mail. So if you have a group in DCE with NetBotz and your user does not have access to that group or does not have an e-mail address associated with it in the server, they will not get the e-mail.

If you're getting the e-mails and do not want them, the only thing you can do at this time is to either remove the user's right to see that device or remove his e-mail from the system. At this time, there is no configuration such as the notification policies that exist for SNMP devices.

 

Steve

(CID:126880915)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

In response to DCIM_Support
0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

Thank you Steve πŸ˜€

(CID:126880925)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

In response to DCIM_Support
0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

Hi Steve

I have a similar query - DCE reports that loss of communication to Netbotz. Version - Netbotz 550 and DCE 7.4.1.

What is troubling is its very VERY random e-mail notifications and the frequency is +/- once a month and at different time intervals. 

Currently we have pinned it to network latency issues considering the default netbotz polling settings. Besides changing/editing these settings what other alternatives are there?

 

Thank you for your time.

(CID:128061134)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

In response to DCIM_Support
0 Likes
0
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

Hi Juice,

It seems as though you've at least partially discovered the reason for the events so if you want to stop receiving the e-mails, you need to either completely resolve the issue (very difficult, especially when it is so intermittent) or you need to remove the e-mail addresses associated with users in DCE. There is nothing to configure that can set a timeout...nothing to be able to group all the messages into one e-mail.

 

Steve

(CID:128061253)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

In response to DCIM_Support
0 Likes
0
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:55 AM . Last Modified: β€Ž2024-04-05 03:40 AM

Hi Steve

Thank you for your feedback.

Since the last communication we had i have received these errors regularly, (""Critical Communication error with device"), and within 2-5 mins the device is online (return to normal).

I have confirmed with network team there are no new changes implemented and no latency issues. DCE (7.4) is monitoring +/- 500 SNMP devices and I get these communication errors from various devices and at random intervals.

The average ping response is between 1 and 10ms. In the interim I have configured SNMP timeout settings from 2s to 5s and retries from 3 to 5 which have resolved the issue, however our client does not approve.

any other possible ideas that I can try ?

thank you for your assistance... very much appreciated.

(CID:128063541)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 02:56 AM . Last Modified: β€Ž2023-10-22 09:35 PM

0 Likes
0
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 02:56 AM . Last Modified: β€Ž2023-10-22 09:35 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore