EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:06 AM . Last Modified: 2024-04-05 04:42 AM
Hi Support Team,
In the NetBotz 250(NBRK0250), what is the power consumption when not using AC Outlet?
Also, if several sensors are connected (excluding SensorPod), will the power consumption increase?
Please tell me if you have any specific specifications.
Thank you.
Tomokazu Yakuwa
(CID:125214135)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:07 AM . Last Modified: 2024-04-05 04:41 AM
Hi Tomokazu Yakuwa,
In accordance with the Installation and Quick Configuration Guide in the "Specifications NetBotz Rack Monitor 250 (NBRK0250)" on page 30, we have:
From the above, it follows that the maximum power consumption of the NetBotz-250 device (regardless of the number of external sensors, the number of connected users (i.e. CPU load), etc.) should not exceed the value:
0.25A * 100Vac = 25W
In addition, the maximum power consumption from the switched outlet should not exceed the value:
10A * 100Vac = 1kW
Let me remind you: in the specifications, the maximum consumed current corresponds to the minimum input voltage and vice versa.
Always glad to answer your questions.
(CID:126158921)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:06 AM . Last Modified: 2024-04-05 04:41 AM
Hi Tomokazu Yakuwa, thanks for posting. Let's hope you find your answer here.
Kind regards Ditte
(CID:126158699)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:06 AM . Last Modified: 2024-04-05 04:41 AM
Hi, Tomokazu Yakuwa,
I suggest you view the following link for technical specifications of NBRK0250
http://www.apc.com/shop/in/en/products/NetBotz-Rack-Monitor-250/P-NBRK0250?isCurrentSite=true
power consumption mentioned is 2400Watts
Thanks,
Navaneethan.R
(CID:126158820)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:06 AM . Last Modified: 2024-04-05 04:41 AM
Hi, Navaneethan,
Thanks for your reply.
But, I think that 2400 Watt is a numerical value including AC Outlet.
(Maybe.. 240V * 10A = 2400Watt)
What I want to know is the power consumption when not using the AC Outlet.
Please tell me this information if you have it.
Regards,
Tomokazu Yakuwa
(CID:126158855)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:07 AM . Last Modified: 2024-04-05 04:41 AM
Hi Tomokazu Yakuwa,
In accordance with the Installation and Quick Configuration Guide in the "Specifications NetBotz Rack Monitor 250 (NBRK0250)" on page 30, we have:
From the above, it follows that the maximum power consumption of the NetBotz-250 device (regardless of the number of external sensors, the number of connected users (i.e. CPU load), etc.) should not exceed the value:
0.25A * 100Vac = 25W
In addition, the maximum power consumption from the switched outlet should not exceed the value:
10A * 100Vac = 1kW
Let me remind you: in the specifications, the maximum consumed current corresponds to the minimum input voltage and vice versa.
Always glad to answer your questions.
(CID:126158921)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:07 AM . Last Modified: 2024-04-05 04:41 AM
I understand it.
Thank you for your support!
Best regards,
(CID:126159053)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:07 AM . Last Modified: 2024-04-05 04:41 AM
Was glad to help 😀.
(CID:126159060)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 12:07 AM . Last Modified: 2023-10-22 09:34 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.