netbotz access logs

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • netbotz access logs
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

0 Likes
8
936
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

netbotz access logs

Please assist

We are using netbotz 4.5.1.

We need to extract a list of access logs for +/- 6months.

 

(CID:126180965)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

I forgot to add - is there anyway that we can extract the appliance logs for +/- 6months.

I am aware that by default, Netbotz hold this info for +/- 24hours.

Please advise.

(CID:126180967)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

0 Likes
5
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi there,

You would need to add additional storage to the NetBotz unit using the External Storage option in Advanced View. Instructions are here.

You should also upgrade the appliance to the latest 4.6.1 BotzWare available here.

Regards

 

(CID:126180981)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi There John

 

Thank you for your speedy response.

We have Netbotz intergrated into DCE therefore we do not need the additional space. I was wondering how could I pull access logs from Netbotz or DCE.

Is there anyway that we can store the 24hour logs over a certain time period ?

(CID:126181024)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:24 AM . Last Modified: ‎2024-04-05 03:50 AM

Hi,

Unfortunately, DCE is unable to store Rack Access logs at the moment, so the only way to see them is in the Appliance Event Log. The only way to view the Appliance Event Log would be to add external storage to the NetBotz appliance itself. There is an enhancement request to add the Rack Access logs to DCE, but I cannot say when this will be available at the moment.

Regards

(CID:126181067)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2024-04-05 03:50 AM

Awesome, thank you John.

Would adding additional space to netbotz allow me to see access logs to the Netbotz device ?

(CID:126181098)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2024-04-05 03:50 AM

Yes, you would see these access logs by going to Tools > Appliance Event Log in Advanced View.

 

(CID:126181157)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2024-04-05 03:50 AM

In response to DCIM_Support
0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2024-04-05 03:50 AM

Great, thank You John.

Will add a windows share and hope to get a view of users accessing Netbotz Appliance.

 

Thank you John - much appreciated.

(CID:126181169)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2023-10-22 09:33 PM

0 Likes
0
935
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:25 AM . Last Modified: ‎2023-10-22 09:33 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore