Hi Nicholas,
Good day!
AP9341 (discontinued) is an extension module for AP9340 (discontinued). It is incompatible with NBRK0550 (Netbotz 550). The compatible sensor pod for the Netbotz 550 is NBPD0150 (NetBotz Rack Sensor Pod 150)