Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-0509:49 PM. Last Modified: 2024-04-0312:41 AM
Hi Nicholas,
Good day!
AP9341 (discontinued) is an extension module for AP9340 (discontinued). It is incompatible with NBRK0550 (Netbotz 550). The compatible sensor pod for the Netbotz 550 is NBPD0150 (NetBotz Rack Sensor Pod 150)