good morning all
is there any way to send a set command to a netbotz 450 to set relais state?
best regards
patrick
(CID:124521784)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:22 PM . Last Modified: β2024-04-07 11:06 PM
Hi Patrick,
I've had a look at this myself, and all the sensors seem to be ready only in the iReasoning MIB Browser. However, i might be wrong, so I will let others comment here, just to confirm.
Regards
(CID:124521841)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:22 PM . Last Modified: β2024-04-07 11:06 PM
thank you john, i have seen this and it is possible to read only over web api but i do not find any way to send command. Customer would like to use it to control the lights in dc. Wish you a nice day.
regards
(CID:124521890)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:22 PM . Last Modified: β2024-04-07 11:06 PM
Hi Patrick,
Nope, John is correct, there is no option to use the SNMP SET command in NetBotz. If you want to manually trigger an event, you'll have to use Advanced View software or in some cases, the NetBotz web interface.
Steve
(CID:124522864)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 10:23 PM . Last Modified: β2023-10-22 09:33 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.