EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:18 PM . Last Modified: β2024-04-03 02:42 AM
I have a netbotz 200 with version 3.7.5.
I need configure authentication for send email, but I can't write my email password.
Thanks.
(CID:143757920)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:18 PM . Last Modified: β2024-04-03 02:42 AM
Hi Jose,
That is an old device and firmware for those systems did not include the option for user name and password for the e-mail server. Sorry but this unit does not have the capability you're looking for. If you have StruxureWare DCE, even the free 5 node version, you can have DCE send the e-mails for you and it has user name / password options. The only other option is to get a new appliance.
Steve
(CID:143758048)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:18 PM . Last Modified: β2024-04-03 02:42 AM
Hi Jose,
To add on what Steve mentioned, the part number of its direct replacement is NBRK0250:
https://www.apc.com/shop/us/en/products/NetBotz-Rack-Monitor-250/P-NBRK0250
This uses the new firmware (v6.XX) that supports SMTP/Email authentication, which is not present with your current Netbotz.
Kind regards,
Justine
(CID:143759193)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 07:18 PM . Last Modified: β2023-10-22 09:33 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.