how to create DCE thresholds of Netbotz fluid and dry contact sensors

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • how to create DCE thresholds of Netbotz fluid and dry contact sensors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:56 PM . Last Modified: ‎2024-04-09 02:08 AM

0 Likes
6
848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:56 PM . Last Modified: ‎2024-04-09 02:08 AM

how to create DCE thresholds of Netbotz fluid and dry contact sensors

Hello,

I have a Netbotz 570 which has some NBES0301 fluid sensors and some dry contact sensors.

When I try to create thresholds of these sensors from DCE I cannot see them. What is the way to do this?

Regards,

 

Enric

 

(CID:104188948)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

0 Likes
2
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

Hi Enric,

To configure Netbotz from DCE, go to Device–>Netbotz Appliance Config–>Alert Settings

See picture below.

 

Regards,
Chris 

(CID:104188951)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

In response to DCIM_Support
0 Likes
0
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

Hi Chris,

I already knew this way but I want to create a threshold from DCE, to include it into a DCE notification policy. It's that possible?

Regards,

 

Enric

 

(CID:104188972)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

In response to DCIM_Support
0 Likes
0
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

Hi Enric, To my knowledge, no, it cannot be done via DCE policy. Netbotz will be sending its alarm by itself (and having its alert policy within netbotz), instead of DCE. Chris

(CID:104188978)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

0 Likes
1
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

Hi Enric,

 

Chris is correct. This can not be done in a DCE policy and must be configured (either through DCE or Advanced View) on the NetBotz appliance itself.

 

The NetBotz version 2 and 3 appliances (not the NB200 or AP9361 rack access) were designed on the old NetBotz and NetBotz Central paradigm. This design was based on the idea of the intelligence "on the edge".  This was so that there would be no single point of failure. If DCE goes down or loses comm with one or more devices, the devices themselves will still be able to alert for themselves. 

 

 Keep in mind that the NetBotz appliance is also able to alert in many more ways than DCE such as output relays etc. Leaving DCE alone to alert would cause the loss of this type of alerting mechanism.  Requests such as this have however come to our attention in the past and product management is aware that some customers would rather have DCE alert as it does for SNMP devices that it monitors. This is something that they may consider in the future but as far as I know, there are no current plans to change the way 7.x DCE and current NetBotz offerings work together.

 

Thanks,

Steve

(CID:104189022)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

In response to DCIM_Support
0 Likes
0
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2024-04-09 02:08 AM

Hi Steve,

Thanks for your extended explanation. I understand the reason to set the Netbotz thresholds inside the Netbotz. I think it's a good option but also was good to set all in DCE so was more easy to put all devices of a room in maintenance mode, for insteance.

Regards,

 

Enric

 

(CID:104863318)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2023-10-31 11:04 PM

0 Likes
0
847
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 05:57 PM . Last Modified: ‎2023-10-31 11:04 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of