Posted: 2024-11-22 01:50 AM
Hello,
I am trying to upgrade an UPS firmware via Ecostructure in one of our remote locations.
I tested SSH and the connection to the device from the IT gateway is fine.
However when I start the firmware upgrade I get :download checksum mismatch error: as you can see in attachment.
Searched on the forums but did not find anything.
Since it is a remote site I cannot do anything via serial cable.
Please advice how I could solve this.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-26 08:21 AM
DCIM Technical Support reports:
We did have a platform issue with the checksum. A hotfix is in place and updates should work for you. If you're still experiencing issues please let me know.
Unfortunately, one site now has a new (also undocumented) problem:
Binary image version mismatch
Sigh...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-26 08:21 AM
DCIM Technical Support reports:
We did have a platform issue with the checksum. A hotfix is in place and updates should work for you. If you're still experiencing issues please let me know.
Unfortunately, one site now has a new (also undocumented) problem:
Binary image version mismatch
Sigh...
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-11-28 01:11 AM
I confirm that I was able to update 1 firmware .
So this is working again.
Thank you !
Link copied. Please paste this link to share this article on your social media post.