could you please guide me how and where to place humidity / temperature sensors within Data Center RACKS. I have two InRow RP and InRow RD units?
(CID:106206329)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:29 AM . Last Modified: β2024-04-08 11:57 PM
Dear Abdullah,
Here are the recommendations to install a temperature sensor(AP9335T) at the racks.
2. Connect the sensor cable to a Universal Sensor Port on a compatible device. The length can be extended via an RJ-45 coupling with CAT-5 cable.
Here are the recommendations to install a temperature and humidity(AP9355TH) sensor at the racks.
Attach sensors to the vertical rail in a rack using adhesive cable tie holders and tie wraps (bottom graphic). Tighten a tie wrap across the sensorβs bottom recessed channel.
Connect the sensor cable to a Universal Sensor Port on a compatible device. The length can be extended via an RJ-45 coupling with CAT-5 cable.
I also suggest you to refer the APC APC Whitepaper #102: Monitoring Physical Threats in the Data Center for more useful information.
I hope this helps.
Regards,
Bala
(CID:106206341)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 03:29 AM . Last Modified: β2023-10-31 10:17 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.