Wireless Sensor Pod 180 and AP9335TH sensor issue

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Wireless Sensor Pod 180 and AP9335TH sensor issue
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

0 Likes
5
1110
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

Wireless Sensor Pod 180 and AP9335TH sensor issue

Hi!

I'm faced with sensor connection issue.

When I connect temperature/humidity  sensor AP9335TH to wireless sensor pod, Netbotz appliance mark it as "Invalid sensor" with N/A readings.

Is it correct behavior? Installation manual tells that AP9335TH are supported, but in fact we cant use it.

There are NBRK0450 with 4.5.1 firmware and NBPD0180 with 1.0.1 firmware in setup. AP9335T sensors works fine.

 

And second question is: How to delete invalid sensor from configuration? Remove button in "Sensors" configuration window is not active.

Only way I've found is :

  1. Disconnect and delete sensor pod
  2. Disconnect sensors
  3. Connect Pod and apply commission list again

Is there an easy way to do it?

 

(CID:106204164)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

0 Likes
3
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Valentin,

 

You should be able to connect the AP9335TH to the NetBotz 180 but the pod will only read temperature and not humidity as per:

http://www.apcmedia.com/salestools/JGAY-8LQRE2/JGAY-8LQRE2_R2_EN.pdf?sdirect=true

APC Temperature & Humidity Sensor (reports temperature only when connected to the Wireless Sensor Pod 180) AP9335TH

 

I would make sure the wireless sensors get upgraded. My bot is running 4.5.1 and I have a 180 attached and it is running version 1.0.5 firmware. You may need to go back to 4.4 to get the 180 pods up to version 1.0.3 and then upgrade to 4.5.1 again. If you have multiple devices, you may want to connect all the 180s to a single NetBotz appliance which you would downgrade to 4.4 and update each pod.

 

Steve

 

 

(CID:106204167)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

0 Likes
3
1112
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Valentin,

 

You should be able to connect the AP9335TH to the NetBotz 180 but the pod will only read temperature and not humidity as per:

http://www.apcmedia.com/salestools/JGAY-8LQRE2/JGAY-8LQRE2_R2_EN.pdf?sdirect=true

APC Temperature & Humidity Sensor (reports temperature only when connected to the Wireless Sensor Pod 180) AP9335TH

 

I would make sure the wireless sensors get upgraded. My bot is running 4.5.1 and I have a 180 attached and it is running version 1.0.5 firmware. You may need to go back to 4.4 to get the 180 pods up to version 1.0.3 and then upgrade to 4.5.1 again. If you have multiple devices, you may want to connect all the 180s to a single NetBotz appliance which you would downgrade to 4.4 and update each pod.

 

Steve

 

 

(CID:106204167)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

Thank you Steve! It's my first wireless installation. I've downgrade Netbotz to 4.4.0 already, but have the same issue and upgrade it back to 4.5.1 I will try to downgrade back again tomorrow. Can you tell me if pods firmware will be installed automatically, or I need to trigger it somehow? Will update process be indicated in Advanced View? Finaly, if I understand correctly, I need: 1. Downgrade appliance to 4.4 Botzware 2. Wait for pod's update their firmware to 1.0.3 3. Upgrade Botzware to 4.5.1 4. Wait for pods update to 1.0.5 firmware 5. Connect T/H sensors Correct me, please if I'm wrong.

(CID:106204168)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Valentin, Yes, that's about the size of it. You should be able to force the upgrade a little quicker with the button in the wireless configuration applet but yes, those are the steps. Steve

(CID:106204169)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
1111
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:50 AM . Last Modified: ‎2024-04-09 12:09 AM

Thank you Steve! I find out, that it is posssible to update pod's firmware without Netbotz downgrade. It takes about 35-40 minutes and there is no any indication about upgrade status. That's a very uncomfortable. But finally AV show that firmware version became 1.0.5, but sensor still "invalid". Then I delete pod from appliance, disconnect sensors, reboot pod and add it to comission list again. After discovery Netbotz show temperature from TH sensor.

(CID:106204251)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:51 AM . Last Modified: ‎2023-10-31 11:45 PM

0 Likes
0
1109
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:51 AM . Last Modified: ‎2023-10-31 11:45 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.