Used Protocols Over the Communication Between ITA & DCE
Dears,
What are the exact protocols used over the communication between ITA & DCE ?
To be more specific,
The FTP protocol is used over the commination flow between DCE server and the data center infrastructure devices (rPDUs, Cooling Units, UPSs, ...etc.) which is a physically separated private network (DCE LAN Port-2).
Is this FTP protocol is used over the communication between the ITA and DCE servers (Customer Public network) ?
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
Accepted Solutions
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-19 08:39 AM
Hi,
Communication between DCE & ITA is HTTPS in the default configuration, or HTTP if so configured.
Data Center Expert Security Handbook – DCIM Support (ecostruxureit.com)
DCO network firewall port details – DCIM Support (ecostruxureit.com)
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-20 01:35 AM . Last Modified: 2021-12-20 01:36 AM
Hi Ashraf,
No, ITA dose not use FTP protocols to communicate with DCE.
ITA uses the webservices calls to communicate with the integrated DCE (as external system), depending on the configuration (user configurable) communications would be via port 80 or 443.
Kind regards,
Jef
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-19 08:39 AM
Hi,
Communication between DCE & ITA is HTTPS in the default configuration, or HTTP if so configured.
Data Center Expert Security Handbook – DCIM Support (ecostruxureit.com)
DCO network firewall port details – DCIM Support (ecostruxureit.com)
- Tags:
- english
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-12-20 01:35 AM . Last Modified: 2021-12-20 01:36 AM
Hi Ashraf,
No, ITA dose not use FTP protocols to communicate with DCE.
ITA uses the webservices calls to communicate with the integrated DCE (as external system), depending on the configuration (user configurable) communications would be via port 80 or 443.
Kind regards,
Jef