EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 07:36 PM . Last Modified: ‎2024-04-04 11:10 PM
I've encountered this error when upgrading 7.3.1 -> 7.4.3. I started the upgrade and the server has been at this screen for about 2 hours. Before this, I added an additional drive as outlined in the FAQ article. I have a snapshot of the machine on 7.3.1 that I can roll back to if need be.
(CID:132657808)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 07:36 PM . Last Modified: ‎2024-04-04 11:10 PM
Dear Jeremiah Shaver,
Tell us, please, could you solve your problem or not?
With respect.
(CID:132662558)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 07:36 PM . Last Modified: ‎2024-04-04 11:10 PM
Yes, I did. Ended up running a backup from within DCE, re-installing the server from new, and restoring from backup. Was able to successfully upgrade after that.
Another admin must have changed the size of the root drive.
(CID:132662809)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 07:36 PM . Last Modified: ‎2024-04-04 11:10 PM
Dear Jeremiah Shaver,
Thanks for the clarification: i.e., your problem as well as many similar ones was due to lack of free space on the DCE-server storage (see for example topics Physical DCE AP9470 to VM and ).
With respect.
(CID:132662851)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-04 07:36 PM . Last Modified: ‎2023-10-22 04:10 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.