EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-07-05 10:48 PM . Last Modified: โ2024-04-03 12:20 AM
We have two stand-alone DCE severs which are polling same devices. I noticed that sometimes the two servers got different data from the same device.
The device is a circuit breaker which communicates with DCE in MODBUS via a power meter gateway. Both servers monitor the breaker state. One server reports the breaker is in OPEN state while another server reports the breakers is in CLOSE state . I tried Request Device Scan and nothing changed.
I tried to deleted the device and add it again, the server then reported correct state.
(CID:149785687)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-07-05 10:48 PM . Last Modified: โ2024-04-03 12:20 AM
Same DDF version Files on both Servers?
(CID:149785696)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-07-05 10:48 PM . Last Modified: โ2024-04-03 12:20 AM
yes, same DDF version files on both servers.
(CID:149785701)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-07-05 10:49 PM . Last Modified: โ2023-10-22 04:08 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.