The UNKNOWN_DEVICE device was detected but is not supported

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • The UNKNOWN_DEVICE device was detected but is not supported
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
9
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

The UNKNOWN_DEVICE device was detected but is not supported

(CID:134030004)

Labels
  • Labels:
  • IT Expert
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
0
1507
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

The above message was the result after running the discovery on a device (UPS).

(CID:134030023)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
0
1508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

Dear John Beck,

To help you faster and better, we need at least to know:

  • the UPS model;
  • the firmware version of the UPS;
  • the firmware version of the NMC (if applicable).

In addition, we need a log-file from the EcoStruxure IT Gateway server, immediately after the above failed discovering.

Please tell us, does the above error occur with all UPSs of one model (or one firmware version), or only with some of them? Previously, when this UPS model was discovered, did this error occur or not?

P.S.: Taking into account your previous topics  and , I strongly recommend that you follow the system requirements for the EcoStruxure IT Gateway software. In addition, there is a suspicion of the possible presence of some problems in your corporate network related to the settings of firewalls or other network equipment.

With respect.

(CID:134030116)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:16 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

Currently they are all online - see below:

(CID:134030586)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

Dear John Beck,

It's good ๐Ÿ˜€.

Based on this, I recommend that you ask your network administrators about the details of setting up firewalls in your corporate network. I mean, the latency in the network, as this is critical for the gateway software.

Also, ask them for you to explain how two your UPS's 10.48.6.46 and 10.48.6.48 are connected to the corporate network (through which firewalls and gateways, etc.). This is important for understanding why they UPS's behave differently?

In addition, I recommend trying to change the DEVICE POLLING settings of your gateway software for SNMP devices. I.e., change Timeout (seconds) and Retries.

Perhaps this will help you.

With respect.

(CID:134030581)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
1
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

John Beck,

 

Thank you for your question. Getting straight to the point.

An Unknown Device, is a device that currently does not have a Device Definition File or DDF. EcoStruxure IT uses the DDF to translate the information that the monitored device is providing to usable data. During the discovery process the gateway will start to receive data from the device and start comparing make and model information to the DDFs that the gateway has preinstalled. If the gateway doesn't have a DDF already installed then the device will not be allowed to be discovered and the Unknown Device error with be present within the Discovery Log.

My first recommendation is to upgrade to the latest version of the gateway because the most up-to-date DDFs are prepackaged within the installer and the gateway. With the latest version of the gateway we also introduced automatic DDF process meaning that you will never have to request a DDF for the gateway. At this time new DDFs are introduced in the next release of the gateway.

Please let me know if you have any additional questions.

 

Thank You

Victor

(CID:134030584)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

In response to DCIM_Support
0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

Dear VSales,

John Beck has the latest version of the gateway software and has an open FTP access to the devices.

With respect.

(CID:134030593)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

Thank you Victor for the explanation (I have been looking for one).  The version of ExoStruxure IT Gateway is as follows:

 

(CID:134030685)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2024-04-04 02:36 AM

Dear John Beck,

Tell us, please, did you solve your problem or not?

With respect.

(CID:134680029)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2023-10-22 04:06 AM

0 Likes
0
1509
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 11:17 PM . Last Modified: โ€Ž2023-10-22 04:06 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of