EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 09:49 AM . Last Modified: β2024-04-08 03:13 AM
Hello Community,
My customer repports some freeze situations with their Struxureware DCE installation, I installed the DCE and activate the 25 node aditional license on past october and after 2 weeks they detects this behaviour, their action was add other three virtual cpu to the DCE server without our guide now the system has 1 GB of ram and 4 CPU, by the way, what kind of information could be necessary in order to get an idea of the isue? when this situation show, the desktop client reports communication isues, the DCE web page donΒ΄t open but the ping answer is ok, any idea for this? Customer has a support contract please confirm if is necesary to repport here the support contract ID.
Best regards,
(CID:110014353)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 09:49 AM . Last Modified: β2024-04-08 03:13 AM
By my experience I will tell, that for the DCE server it is better to add the RAM at least to 3-4 GB than processors.
Besides, you can download log files of the DCE server and analyze them about loading of processors and memory: .
Very thanks for the support.
(CID:110014360)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 09:49 AM . Last Modified: β2024-04-08 03:13 AM
By my experience I will tell, that for the DCE server it is better to add the RAM at least to 3-4 GB than processors.
Besides, you can download log files of the DCE server and analyze them about loading of processors and memory: .
Very thanks for the support.
(CID:110014360)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 09:49 AM . Last Modified: β2024-04-08 03:12 AM
Thank you very much for your commentary I hope to visit this customer on next week ant take the logs for analyze it.
Best Regards,
Erlinson Bravo G.
(CID:110014605)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-03 09:49 AM . Last Modified: β2023-10-22 04:02 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.