Hi Everybody.
I have a problem for about Diris A40 v3 Energy Analyser. I did add Analyser(Modbus-TCP) to DCE successfully. But DCE read EA value is wrong. When I check value EA Web Interface kw L1:1.09, L2: 1,33, L3:1,14, But on DCE, values is wrong. L1:42.232.123, L2: 1,66, L3:42.125.452. How can i fix it?
Thanks.
(CID:107448577)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 AM . Last Modified: 2024-04-08 11:24 PM
Hi Alper,
I'm not familiar with the Diris A40 v3 Energy Analyser, I'm assuming you received a DDF file for this device using either the multiendorsupport@apc.com e-mail address or the device support option on this EcoStruxure IT Help Center page. In either case, I believe what you're likely seeing is either DCE is polling the wrong register or it is formatting it incorrectly. I believe that you'll need to speak with the people that created the DDF and they'll likely need to use different registers or rearrange the registers to format the output correctly.
Steve
(CID:107448583)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 AM . Last Modified: 2024-04-08 11:24 PM
Hi Alper,
I'm not familiar with the Diris A40 v3 Energy Analyser, I'm assuming you received a DDF file for this device using either the multiendorsupport@apc.com e-mail address or the device support option on this EcoStruxure IT Help Center page. In either case, I believe what you're likely seeing is either DCE is polling the wrong register or it is formatting it incorrectly. I believe that you'll need to speak with the people that created the DDF and they'll likely need to use different registers or rearrange the registers to format the output correctly.
Steve
(CID:107448583)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 AM . Last Modified: 2024-04-08 11:24 PM
Hi Alper you have two way 1 - reset eternet getway or EGX 2 - change ddf file maybe your ddf is wrong please send email for multivendors
(CID:107448599)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 AM . Last Modified: 2024-04-08 11:24 PM
Hi Alper. I struggled for a long time with this too.
It turns out that at some point in time Socomec changed the MODBUS table addresses on the Diris A40 Power Meter.
We have had two DDF files (both supplied by Schneider / multivendorsupport), one for the old version and one for new version
I know that the DDF V3 works for the older units as we have one of those deployed.
I have not been able to test the other DDF file on the newer Diris A40
Files below:-
socomec_diris_a40_power_meter.xml
socomec_diris_a40 Old (V3).xml
Hopefully one of these will cure the issue.
Regards
(CID:107448615)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 05:16 AM . Last Modified: 2023-10-31 11:36 PM