EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:08 PM . Last Modified: 2024-04-07 11:58 PM
Hello,
Did someone add a smartlink gateway A9XMWA20 in DCE 7.4 for reading data from PowerTag A9MEM1520 power meters?
I need to do it for monitoring the load of a datacenter with more than 60 circuit breakers in one panel and it is not possible to use bigger power meters because of lack of space.
I was not able to find a driver for A9XMWA20, so if someone can help me it would be very good 😀
(CID:122691599)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:08 PM . Last Modified: 2024-04-07 11:58 PM
Hi,
There is already smartlink DCE DDF for modbus TCP:
https://dcimsupport.apc.com/devices/view/Acti9%20Smartlink%20Modbus/Schneider%20Electric
Give it a try, and contact device support if you need to get any modification done on the DDF.
(CID:122691618)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:08 PM . Last Modified: 2024-04-07 11:58 PM
Hello,
The smartlink is not the same model and the driver I need is actually for the power meter A9MEM1520, not the gateway itself.
I will contact the device support for this topic.
Here is the modbus register list for the A9MEM15xx devices in Smartlink Si 😧
Acti 9 Smartlink SI D - Device Registers.pdf
Thank you
(CID:122691639)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:08 PM . Last Modified: 2024-04-07 11:58 PM
Hi,
Did the ddf for power tag get created as I can not see it in the list of supported devices, and I also have the same use case.
Andy
(CID:130094109)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:08 PM . Last Modified: 2023-10-22 03:56 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.