Posted: 2020-07-03 06:08 PM . Last Modified: 2024-04-07 11:58 PM
For some reason I am having issues with discovering APC UPS devices. I have Netbotz devices on the same network that are discoverable without a problem. Is there a special process for discovering the UPS devices?
Some things I've already checked:
Any ideas?
(CID:122691842)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:08 PM . Last Modified: 2024-04-07 11:58 PM
you should be doing an snmp v1 or v3 discovery, the snmp community strings in your discovery need sto match whats on the device under Network-->SNMPv1–>access control, also if the nms ip isn't all 0's, you need either need to add DCE's ip to one of the other access control fields, eg 3 and or 4, or if the nms ip is in the same subnet as dce (eg both are on 10,0.1.x), you could change the last octet to a .255, 10.1.0.255.
some other possible issues are snmp is blocked between DCE and the UPS device and or you're out of licenses. I have all seen some weird issues in more recent versions where you need to restart the DCE client to see new devices, but thats rare.
worst case, call your local tech support, US is 877-908-2688 and have them help you troubleshoot.
(CID:122691849)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:08 PM . Last Modified: 2024-04-07 11:58 PM
you should be doing an snmp v1 or v3 discovery, the snmp community strings in your discovery need sto match whats on the device under Network-->SNMPv1–>access control, also if the nms ip isn't all 0's, you need either need to add DCE's ip to one of the other access control fields, eg 3 and or 4, or if the nms ip is in the same subnet as dce (eg both are on 10,0.1.x), you could change the last octet to a .255, 10.1.0.255.
some other possible issues are snmp is blocked between DCE and the UPS device and or you're out of licenses. I have all seen some weird issues in more recent versions where you need to restart the DCE client to see new devices, but thats rare.
worst case, call your local tech support, US is 877-908-2688 and have them help you troubleshoot.
(CID:122691849)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:09 PM . Last Modified: 2024-04-07 11:58 PM
Did not realize I needed to use SNMP for the UPS devices. Thanks!
(CID:122691928)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 06:09 PM . Last Modified: 2023-10-22 02:24 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.