SNMP Comunication

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • SNMP Comunication
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
63
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

0 Likes
4
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

SNMP Comunication

I have some rack PDU's reporting to the Austin Hughes IPM softwere. the snmp walk program is not returning any values it says it failed to respond: 

but i can run snmp test no issues

when i try to add the device as an SNMPv1 device DCE wont even find it. looking at the logs on the machine, both DCE and the snmp walk program are searching for OID's that don't exist on the device 

Has anyone else come across this issue??

TIA

Mike

(CID:129412316)

Labels
  • Labels:
  • Data Center Expert
Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

0 Likes
0
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

Dear mike sutton,

Can you describe in more detail which device of what vendor are you trying to add to the DCE software?

In addition, your screenshot has a very small size and a small resolution. Because of this, it's simply impossible to see anything on it. Can you please show us the screenshot with the normal size and resolution?

With respect.

(CID:129412597)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

0 Likes
0
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

Hi,

I am trying to add austin hughes infrapower manager to DCE but as you can see on this pic DCE is going for OID's that dont exist main pic snmp test ignore the ip its just a loop back on the machine the software is running on. so the OID should start with 1.3.6.1.4.1.36402. but if you look at wire shark you can see when i tried to add it DCE was looking for OID 1.3.6.1.2.1.1.2.0 

What im trying to understand is what is telling DCE to start at that OID?

Cheers,

 

Mike

(CID:130091580)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

0 Likes
0
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2024-04-05 12:27 AM

Dear mike sutton,

In order for the DCE server to know how to communicate with your 3rd party equipment (via SNMP or TCP/IP Modbus protocol), a special DDF-file is required.

Do you have a DDF-file on the DCE server for Austin Hughes IPM equipment?

As far as I know, neither DCE nor DCO software currently not supports Austin Hughes IPM equipment. This can easily be checked with Device Support. Therefore, it's not surprising, that your DCE server simply does not find your 3rd party equipment.

If you have any further questions, please ask.

With respect.

(CID:130091578)

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2023-10-22 03:49 AM

0 Likes
0
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:47 PM . Last Modified: ‎2023-10-22 03:49 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply
Contact Support

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of