EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:53 PM . Last Modified: β2024-04-05 02:30 AM
I have a nrbk570 appliance, 4 CP160 connected to it,. Physical DCE licensed the cameras but when i retrive clips nothing show up. Client is running on windows 7.
Thanks in advance.
(CID:129404108)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:53 PM . Last Modified: β2024-04-05 02:30 AM
Hi Marcio,
The first thing to look at are the dates and times of the DCE server and NetBotz appliance (Assuming they're in the same region) as if they are out of sync, DCE may not show clips when you are looking for a certain time (last hour etc). To verify this, you can use the "Range" option instead of "Last Hour" or day. If the NetBotz appliance is ahead of DCE by an hour, you may need to look in the future as DCE sees it. Use a range of yesterday to tomorrow for instance.
Other than that, you'd need to check surveillance settings. How is it set to surveil? On motion? On motion during alerts? Is the NetBotz alerting? There are a few different things to look at here to see if you're even supposed to be getting clips.
Steve
(CID:129404226)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:53 PM . Last Modified: β2024-04-05 02:30 AM
Hi steve!
thanks for your reply, i will recheck and return to you.
regards
(CID:129406556)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:53 PM . Last Modified: β2024-04-05 02:30 AM
Hi steve.
Everything is fine now. i just restarted the NBRK and the DCE, and started to retrieve
Regards
(CID:129406553)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-04 02:53 PM . Last Modified: β2023-10-22 03:44 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.