Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84784members
354230posts

Rack Monitor NetBotz 250: Clock Accuracy

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
rf2019
Lieutenant JG
Lieutenant JG
0 Likes
5
2242

Rack Monitor NetBotz 250: Clock Accuracy

Hello,

 

I am working on a system on which the time accuracy is key.

I would like to know:

  1. what is the clock accuracy of the Rack Monitor NetBotz 250 ?
  2. If I configure via ssh the date&time what will the clock accuracy be ?

I cannot find this information in the documentation.

 

Thank you in advance.

Best Regards,

 

Raphaël

Tags (1)

Accepted Solutions
Rick_O
Lieutenant JG Lieutenant JG
Lieutenant JG

Re: Rack Monitor NetBotz 250: Clock Accuracy

@rf2019 From our Hardware folks.

 

The crystal is the main spec, it’s 10ppm. It is a hardware timer, so it’s not software dependent. There are 2.7M seconds in a month so the crystal alone is 27 seconds/month. As a rule of thumb we generally say it generally is “a minute a month”.

 

All that being said something important to note is that we only time stamp to the second, so accuracy better than 1 second is not going to be reflected in log entries.

 

Thanks,
Rick

See Answer In Context

Tags (1)
5 Replies 5
Valentin_Kozlov
Lieutenant Lieutenant
Lieutenant
0 Likes
4
2229

Re: Rack Monitor NetBotz 250: Clock Accuracy

Hi Raphael!

 

Maybe someone from product team have info about clock accuracy, but there is no info in open documentation.

In terms of usual operation it is pretty accurate, but it's recomended to set up communication with NTP server for periodic time syncronization.

Tags (1)
rf2019
Lieutenant JG
Lieutenant JG
0 Likes
3
2218

Re: Rack Monitor NetBotz 250: Clock Accuracy

Hello Valentin,

 

I did not find any information either in the documentation.

 

However, the NTP cannot be used and I need to assess the accuracy of the time clock, and as well as the amount of time after which the accuracy is drifting, so the system will reconnect to the APC Sensors and update the date&time.

 

I looking forward to reading from the product team. Will they answer to this feed ?

 

Best Regards,

 

Raphaël

Tags (1)
JLehr
Lt. Commander Lt. Commander
Lt. Commander
0 Likes
0
2209

Re: Rack Monitor NetBotz 250: Clock Accuracy

Hi @rf2019,

 

I'll see what I can do to get some eyes on this.

 

Jackie

Tags (1)
Rick_O
Lieutenant JG Lieutenant JG
Lieutenant JG

Re: Rack Monitor NetBotz 250: Clock Accuracy

@rf2019 From our Hardware folks.

 

The crystal is the main spec, it’s 10ppm. It is a hardware timer, so it’s not software dependent. There are 2.7M seconds in a month so the crystal alone is 27 seconds/month. As a rule of thumb we generally say it generally is “a minute a month”.

 

All that being said something important to note is that we only time stamp to the second, so accuracy better than 1 second is not going to be reflected in log entries.

 

Thanks,
Rick

Tags (1)
rf2019
Lieutenant JG
Lieutenant JG
0 Likes
0
2193

Re: Rack Monitor NetBotz 250: Clock Accuracy

Thank you so much for your explanation Rick ! 😁

Tags (1)