Rack Monitor Netbotz 250 : Syslog Severity Configuration

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Rack Monitor Netbotz 250 : Syslog Severity Configuration
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Anonymous user
Not applicable

Posted: ‎2020-11-16 03:23 AM

0 Likes
4
2730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-16 03:23 AM

Rack Monitor Netbotz 250 : Syslog Severity Configuration

Hello,

I am currently working on the Syslog severity of the Rack Monitor NetBotz 250 and after reading the User Manual and the Configuraiton file (.ini), I have questions regarding the Severity level of my syslog.

 

[NetworkSYSLOG]
Syslog=enabled
Facility=User
Server1=0.0.0.0
Server2=0.0.0.0
Server3=0.0.0.0
Server4=0.0.0.0
Port1=514
Port2=514
Port3=514
Port4=514
Protocol1=1
Protocol2=0
Protocol3=0
Protocol4=0
Language1=enUs
Language2=enUs
Language3=enUs
Language4=enUs
SyslogMapCritical=Info
SyslogMapWarning=Warning
SyslogMapInformational=Info

 

What are the differences between SyslogMapCritical, SyslogMapWarning and SyslogMapInformational.

If I want to have a Debugging severity level, where should I input the value ?

 

Thank you in advance.

Best Regards,

 

Raphaël

Labels
  • Labels:
  • DDF
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Valentin_Kozlov
Lieutenant Valentin_Kozlov Lieutenant
Lieutenant

Posted: ‎2020-11-17 04:08 AM . Last Modified: ‎2020-11-17 04:12 AM

In response to Anonymous user
1 Like
1
2703
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-17 04:08 AM . Last Modified: ‎2020-11-17 04:12 AM

Raphael you may refer to RFC to get more deep Syslog description.

 

Each Syslog message have PRI field which comes after header and means emergency level of the message.

The Priority value is calculated by first multiplying the Facility
   number by 8 and then adding the numerical value of the Severity.  For
   example, a kernel message (Facility=0) with a Severity of Emergency
   (Severity=0) would have a Priority value of 0.  Also, a "local use 4"
   message (Facility=20) with a Severity of Notice (Severity=5) would
   have a Priority value of 165.  In the PRI of a syslog message, these
   values would be placed between the angle brackets as <0> and <165>
   respectively. 

 

I'm not sure what exact Facility code Netbotz use for Syslog messages.

 

Let's imagine that it will "local use 4" as in example above with Facility=20.

 

Then we map our Netbotz messages to Syslog Severity:

 

SyslogMapCritical=Critical

SyslogMapWarning=Warning

SyslogMapInformational=Info

 

As per FRC table

       Numerical         Severity
             Code

              0       Emergency: system is unusable
              1       Alert: action must be taken immediately
              2       Critical: critical conditions
              3       Error: error conditions
              4       Warning: warning conditions
              5       Notice: normal but significant condition
              6       Informational: informational messages
              7       Debug: debug-level messages

 

 

SyslogMapCritical=Critical => 2

SyslogMapWarning=Warning => 4

SyslogMapInformational=Info => 6

 

So you will receive PRIVAL=162 (Facility*8+Severity = 20*8+2) in case of Critical Netbotz alert, PRIVAL=164 (Facility*8+Severity = 20*8+4) in case of Warning alert and PRIVAL=166 (Facility*8+Severity = 20*8+6) for Informational events.

 

Considering this numbers you can work with messages on your Syslog server.

 

If you set

 

SyslogMapCritical=Info => 6

SyslogMapWarning=Info => 6

SyslogMapInformational=Info => 6

 

All messages from Netbotz will have equal priority level PRIVAL=166 (Facility*8+Severity = 20*8+6) for syslog server.

 

If you would like to receive Debugging severity level for all events from Netbotz, you should set this level for all alert types^

SyslogMapCritical=Debug

SyslogMapWarning=Debug

SyslogMapInformational=Debug

 

 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
Valentin_Kozlov
Lieutenant Valentin_Kozlov Lieutenant
Lieutenant

Posted: ‎2020-11-17 12:11 AM

0 Likes
3
2712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-17 12:11 AM

Hi Raphael!

 

Netbotz have three levels of severity - Informational, Warning and Critical.

In described section you can map Netboz levels to desired Syslog levels.

 

As per RFC3164 there are eight levels:

        Numerical         Severity
          Code

           0       Emergency: system is unusable
           1       Alert: action must be taken immediately
           2       Critical: critical conditions
           3       Error: error conditions
           4       Warning: warning conditions
           5       Notice: normal but significant condition
           6       Informational: informational messages
           7       Debug: debug-level messages

 

In your example when Netbotz register Warning alarm, you will receive syslog message with "warning" severity level, in other two cases you will receive messages with  "informational" severity level.

 

It is just a way to prioritize messages from Netboz on your Syslog server.

 

You will not receive more detailed message if you set "debug" level there.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-17 01:54 AM

In response to Valentin_Kozlov
0 Likes
2
2707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-17 01:54 AM

Hi Valentin,

Thank you for your reply.

I understand that there are only three severity level for the NetBotz.

However, I still have difficulties to understand what the three parameters are about:

  • SyslogMapCritical
  • SyslogMapWarning
  • SyslogMapInformational

 

Thank you in advance.

Best Regards,

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Valentin_Kozlov
Lieutenant Valentin_Kozlov Lieutenant
Lieutenant

Posted: ‎2020-11-17 04:08 AM . Last Modified: ‎2020-11-17 04:12 AM

In response to Anonymous user
1 Like
1
2704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-17 04:08 AM . Last Modified: ‎2020-11-17 04:12 AM

Raphael you may refer to RFC to get more deep Syslog description.

 

Each Syslog message have PRI field which comes after header and means emergency level of the message.

The Priority value is calculated by first multiplying the Facility
   number by 8 and then adding the numerical value of the Severity.  For
   example, a kernel message (Facility=0) with a Severity of Emergency
   (Severity=0) would have a Priority value of 0.  Also, a "local use 4"
   message (Facility=20) with a Severity of Notice (Severity=5) would
   have a Priority value of 165.  In the PRI of a syslog message, these
   values would be placed between the angle brackets as <0> and <165>
   respectively. 

 

I'm not sure what exact Facility code Netbotz use for Syslog messages.

 

Let's imagine that it will "local use 4" as in example above with Facility=20.

 

Then we map our Netbotz messages to Syslog Severity:

 

SyslogMapCritical=Critical

SyslogMapWarning=Warning

SyslogMapInformational=Info

 

As per FRC table

       Numerical         Severity
             Code

              0       Emergency: system is unusable
              1       Alert: action must be taken immediately
              2       Critical: critical conditions
              3       Error: error conditions
              4       Warning: warning conditions
              5       Notice: normal but significant condition
              6       Informational: informational messages
              7       Debug: debug-level messages

 

 

SyslogMapCritical=Critical => 2

SyslogMapWarning=Warning => 4

SyslogMapInformational=Info => 6

 

So you will receive PRIVAL=162 (Facility*8+Severity = 20*8+2) in case of Critical Netbotz alert, PRIVAL=164 (Facility*8+Severity = 20*8+4) in case of Warning alert and PRIVAL=166 (Facility*8+Severity = 20*8+6) for Informational events.

 

Considering this numbers you can work with messages on your Syslog server.

 

If you set

 

SyslogMapCritical=Info => 6

SyslogMapWarning=Info => 6

SyslogMapInformational=Info => 6

 

All messages from Netbotz will have equal priority level PRIVAL=166 (Facility*8+Severity = 20*8+6) for syslog server.

 

If you would like to receive Debugging severity level for all events from Netbotz, you should set this level for all alert types^

SyslogMapCritical=Debug

SyslogMapWarning=Debug

SyslogMapInformational=Debug

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-11-17 04:15 AM

In response to Valentin_Kozlov
0 Likes
0
2699
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-17 04:15 AM

Thank you for your explanations 🙂

Best Regards,

 

Raphaël

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of