Rack Access PX-HID AP9361

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Rack Access PX-HID AP9361
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

0 Likes
7
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

Rack Access PX-HID AP9361

Hi All,

 

Not strictly a DCIM-related question but wondered if anyone had experience of the configuration of the APC PX-HID system AP9361. Can't find any answers to these in the product documents.

 

I am familiar with the Netbotz 570 / Access Pod 170 system, but trying to decide which of the two systems is the best option to use for a 40-rack deployment including DCE & DCO.

 

Had a few questions on the AP9361:

 

1 - When configuring an HID card (a set of users) for an AP9361, can that configuration be shared amongst multiple racks like the Netbotz equivalent? If not, this won't be a good option as configuring the same users card 40x times on each rack isn't a clean option.

 

2 - If the configuration can be shared between AP9361, how is this done? Don't really like the idea of needing to manually share a config.ini file across multiple devices, is there a method in the interface of the AP9361 to group multiple devices together?

 

3 - Finally, is there any global control functionality in DCE for the AP9361? - Such as remote open etc

 

Thanks

(CID:97485508)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

0 Likes
4
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

Hi David,

 

Mike answered the config part. DCE can do it (direct config or with a template), it can use radius ( Free radius only, k-base FA156100) or, as you're aware and apparently don't want to do, share the config.ini. A caveat about the ini which DCE does also push to configure this device, If all 20 card slots are full, they must be refilled with blanks before they can be associated with a new card. 

 

As for remotely unlocking the door, there is the UI, you can use DCE to command the door to unlock, or you can use SNMP. Not sure what you meant by globally, only one command at a time. You can't say for instance  "unlock all doors" unless you create a command file using individual SNMP sets to do so. Please note you can not use SNMP when using the rack access pod 170 and higher level NetBotz appliances. 

 

Steve

(CID:97485533)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

Hi David,

As you are using DCE you can configure a single Rack Access kit with all the HID cards and then use this as a template within DCE using the APC SNMP device configuration tab then the create template option and select the required fields that will apply to all devices such as DNS settings, registered cards e.t.c. save this then select configure from template and apply this to all the relevant rack access kits.

If you use a RADIUS server for door access this can be utilized so building HID cards can be used and authenticated.

 

Hope this helps

 

Mike 

(CID:97485530)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

0 Likes
4
957
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

Hi David,

 

Mike answered the config part. DCE can do it (direct config or with a template), it can use radius ( Free radius only, k-base FA156100) or, as you're aware and apparently don't want to do, share the config.ini. A caveat about the ini which DCE does also push to configure this device, If all 20 card slots are full, they must be refilled with blanks before they can be associated with a new card. 

 

As for remotely unlocking the door, there is the UI, you can use DCE to command the door to unlock, or you can use SNMP. Not sure what you meant by globally, only one command at a time. You can't say for instance  "unlock all doors" unless you create a command file using individual SNMP sets to do so. Please note you can not use SNMP when using the rack access pod 170 and higher level NetBotz appliances. 

 

Steve

(CID:97485533)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

In response to DCIM_Support
0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

HI Steve! What do you mean when you wrote about creating a command file? Is there feature that allow to run some scripts on DCE?

(CID:97485566)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

In response to DCIM_Support
0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

Hi Valentin, No, I was referring to outside of DCE. For instance, you could create an SNMP command line option using something like the utilities found on sourceforge: http://net-snmp.sourceforge.net/tutorial/tutorial-5/commands/snmpset.html You can create a batch or command file that runs multiple commands as seen on that page. This would be up to you . Steve

(CID:97485567)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

In response to DCIM_Support
0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

Thanks for explanation!

(CID:97485579)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

In response to DCIM_Support
0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2024-04-09 04:38 AM

Hi Steve, Thanks for your explanation. Yes, I meant to ask whether the AP9631 could be remotely unlocked from DCE via SNMP, 'global' was a poor choice of words 🙂 I think we'll go down the route of a 570 with 170 sensor pods - the idea is to make configuration as straight-forward as possible for the end users, there will be a number of them and they will want to configure multiple racks at once. David

(CID:97485609)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2023-10-31 11:32 PM

0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:11 PM . Last Modified: ‎2023-10-31 11:32 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of