NetBotz Device Monitoring (Five Nodes) Pack

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NetBotz Device Monitoring (Five Nodes) Pack
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

0 Likes
5
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

NetBotz Device Monitoring (Five Nodes) Pack

Hi Team,

Kindly advise the monitoring options involved in the NetBotz Device Monitoring (Five Nodes) Pack license for servers.

I have a customer who wants to achieve shutdown of servers when the temperature goes well beyond the recommeded threshold.

Is there a solution for this? How can I achieve it?

Regards,

Felix

(CID:97485492)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

Hi Felix,

The device monitoring node pack is to scan SNMP devices, you can't shutdown servers in this way.

If you have an APC UPS, the easiest way to action this is to connect a temperature sensor to an NMC with environmental monitoring, and use Powerchute Network Shutdown installed on the servers mapped to a high temperature event on the card.

(CID:97485515)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

0 Likes
0
642
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

Hi Felix,

The device monitoring node pack is to scan SNMP devices, you can't shutdown servers in this way.

If you have an APC UPS, the easiest way to action this is to connect a temperature sensor to an NMC with environmental monitoring, and use Powerchute Network Shutdown installed on the servers mapped to a high temperature event on the card.

(CID:97485515)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

0 Likes
2
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:39 AM

Hi Felix,

 

On the SNMP side, David is correct, we do not offer control options. The 5 node device pack however also allows the addition of IPMI devices. If the server has a BMS card (or whatever the vendor is calling it) for IPMI communications and that card supports options such as soft reboot, etc, During addition of the IPMI device, you have the option to add these as sensors if available on the target system:

 

You can then right click the sensor to see it has the option to power off:

 

Once you have that configured, you can create an alert action:

Finally, simply ad the action to a profile to initiate the shutdown based upon whatever threshold you'd like. Please be careful, you don't want to turn a system off for invalid reasons, You need to be careful with this one.

 

Steve

 

(CID:97485544)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:38 AM

In response to DCIM_Support
0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:38 AM

Hi Steve, Thanks for this, I had no idea there was an option to trigger a Soft Power-Down from a Netbotz appliance connected to a BMC card. This is useful info to remember for the future

(CID:97485610)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:38 AM

In response to DCIM_Support
0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2024-04-09 04:38 AM

Hey Guys, Thanks a lot for your vaulable contributions. I have learnt something. Regards, Felix

(CID:97485662)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2023-10-31 11:25 PM

0 Likes
0
641
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:10 PM . Last Modified: ‎2023-10-31 11:25 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

https://idp-uat.se.com/authorize?client_id=llTc0ylhBFgpdEXCVkUDxpSio7Ckisb9&redirect_uri=https%3A%2F%2Fuat-community.se.com%2Fauth%2Foauth2callback&response_type=code&scope=openid+name+given_name+family_name+nickname+email+email_verified&referer=https%3A%2F%2Fcommunity.se.com%2Ft5%2FEcoStruxure-IT-forum%2FNetBotz-Device-Monitoring-Five-Nodes-Pack%2Ftd-p%2F203917%3Fsubscribe&screen_hint=signup
Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of