Hi Team,
Kindly advise the monitoring options involved in the NetBotz Device Monitoring (Five Nodes) Pack license for servers.
I have a customer who wants to achieve shutdown of servers when the temperature goes well beyond the recommeded threshold.
Is there a solution for this? How can I achieve it?
Regards,
Felix
(CID:97485492)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:10 PM . Last Modified: 2024-04-09 04:39 AM
Hi Felix,
The device monitoring node pack is to scan SNMP devices, you can't shutdown servers in this way.
If you have an APC UPS, the easiest way to action this is to connect a temperature sensor to an NMC with environmental monitoring, and use Powerchute Network Shutdown installed on the servers mapped to a high temperature event on the card.
(CID:97485515)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:10 PM . Last Modified: 2024-04-09 04:39 AM
Hi Felix,
The device monitoring node pack is to scan SNMP devices, you can't shutdown servers in this way.
If you have an APC UPS, the easiest way to action this is to connect a temperature sensor to an NMC with environmental monitoring, and use Powerchute Network Shutdown installed on the servers mapped to a high temperature event on the card.
(CID:97485515)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:10 PM . Last Modified: 2024-04-09 04:39 AM
Hi Felix,
On the SNMP side, David is correct, we do not offer control options. The 5 node device pack however also allows the addition of IPMI devices. If the server has a BMS card (or whatever the vendor is calling it) for IPMI communications and that card supports options such as soft reboot, etc, During addition of the IPMI device, you have the option to add these as sensors if available on the target system:
You can then right click the sensor to see it has the option to power off:
Once you have that configured, you can create an alert action:
Finally, simply ad the action to a profile to initiate the shutdown based upon whatever threshold you'd like. Please be careful, you don't want to turn a system off for invalid reasons, You need to be careful with this one.
Steve
(CID:97485544)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:10 PM . Last Modified: 2024-04-09 04:38 AM
Hi Steve, Thanks for this, I had no idea there was an option to trigger a Soft Power-Down from a Netbotz appliance connected to a BMC card. This is useful info to remember for the future
(CID:97485610)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:10 PM . Last Modified: 2024-04-09 04:38 AM
Hey Guys, Thanks a lot for your vaulable contributions. I have learnt something. Regards, Felix
(CID:97485662)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 01:10 PM . Last Modified: 2023-10-31 11:25 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Welcome to your new personalized space.
of