EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:25 AM . Last Modified: 2024-04-08 11:58 PM
Hello
I have problem with some sensors on NetBotz 200 / 150. Sometimes the temperature falls down to 0 and came up after some minutes without raseons. Any idea?
Module: V 3.7.5
Best regards.
Rocchino
(CID:106206070)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:25 AM . Last Modified: 2024-04-08 11:58 PM
Hi Rocchino,
If this is happening to one sensor, I would suggest swapping the sensor to another unit or potential another port. If the issue follows the sensor, it sounds like an issue with the sensor.
Is the issue actually happening on a NetBotz 200. The graph however appears to be either a different type of NetBotz appliance (3xx,4xx,5xx) or from a DCE server.If this is being seen in DCE, have you checked the device directly? Is the issue only being seen in DCE? That could be a comms issue.
Steve
(CID:106206096)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:25 AM . Last Modified: 2024-04-08 11:58 PM
Hello Steve,
no the problem is on many sensors connected on Netbotz 200 and Netbotz 150.
The 0 values are also in the netbotz log not only in DCE.
Best regards
Rocchino
(CID:106209673)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:25 AM . Last Modified: 2024-04-08 11:58 PM
Hi Rocchino, If all the sensors are doing it, I would disconnect everything and reset the 200 to defaults. Connect sensors to the main unit. If they're working, then one by one connect the 150s and their sensors. Potentially one of the pods, sensors, or cables is causing this issue. Otherwise, it would appear to be the unit. Steve
(CID:106209674)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:25 AM . Last Modified: 2024-04-08 11:58 PM
Hello Steve, I did some test. I have switched 2 sensors (one with error and one ok) from Netbotz 150 and Netbotz 200. The problem is the same. I think it's a sensor problem... I will try your option (remove, rebot) Tks and best regards Rocchino
(CID:106209675)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:25 AM . Last Modified: 2023-10-31 11:31 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.