Netbotz sensors accuracy

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz sensors accuracy
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

0 Likes
8
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Netbotz sensors accuracy

Hi Team!

Is there any official info about Netbotz temperature and humidity sensors accuracy?

There is no info on apc.com, working range only.

I met info about +/- 2 degrees somewhere, but I'm not sure...

Any help will be appreciated.

(CID:105469530)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

0 Likes
1
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Hi Valentin,

                  kindly see the below k-base link for more information.

K-base ID: FA158170

http://www.apc.com/site/support/us/en/faq/?page=content&country=ITB〈=en&locale=en_US&id=FA158170&red...

          
Temperature sensor Accuracy: + or – 1.8F + or – 1C 
Humidity sensor Accuracy: + or – 5% RH
Dew Point sensor Accuracy: + or - 2 degrees F 
Airflow sensor Accuracy: + or – 50 fpm .

BR,

Rana Ajmal

(CID:105469536)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

0 Likes
1
1201
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Hi Valentin,

                  kindly see the below k-base link for more information.

K-base ID: FA158170

http://www.apc.com/site/support/us/en/faq/?page=content&country=ITB〈=en&locale=en_US&id=FA158170&red...

          
Temperature sensor Accuracy: + or – 1.8F + or – 1C 
Humidity sensor Accuracy: + or – 5% RH
Dew Point sensor Accuracy: + or - 2 degrees F 
Airflow sensor Accuracy: + or – 50 fpm .

BR,

Rana Ajmal

(CID:105469536)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Thank you Rana! It's for v2 internal sensors. Will it be valid for AP9335?

(CID:105469539)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

0 Likes
4
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Hi Valentin,

 

The info is sort of spread out. For the older version 2 NetBotz, k-base FA158170 has some info. In most cases for version 3 sensors, there are accuracy statements in the install or user guide. For instance for the AP9335T:

http://www.apcmedia.com/salestools/ASTE-6Z5QD2/ASTE-6Z5QD2_R0_EN.pdf?sdirect=true

Temperature accuracy ±3ºF (±2ºC), from 32 to 104ºF (0 to 40ºC)


For the NBWS100H, It's on the product page listed under range:

http://www.apc.com/shop/us/en/products/NetBotz-Wireless-Temperature-Humidity-Sensor/P-NBWS100H

 

Sensor Humidity Range

±3% RH from 11% to 89% RH %


I know it can be difficult to find. If you have a specific sensor you can't find info on, we can see if we can find it for you. I know the whole site is being changed around.


Steve

(CID:105469540)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Thank you Steve!

(CID:105469541)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Welcome 😃

(CID:105469542)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

It's not enough clear to me to find sensors specification in docs for discontinued expansion module 😄

(CID:105469543)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

In response to DCIM_Support
0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:22 AM . Last Modified: ‎2024-04-09 12:37 AM

Hi Valentin, If you're referring to the sensor pod 120s, the accuracy would be the same as the stand-alone sensors listed in the k-base. If you're referring to something else, can you please specify? Steve

(CID:105469544)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:23 AM . Last Modified: ‎2023-10-31 11:26 PM

0 Likes
0
1200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:23 AM . Last Modified: ‎2023-10-31 11:26 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore