Netbotz not always sending a proper attachment

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz not always sending a proper attachment
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:29 PM . Last Modified: ‎2024-04-09 01:12 AM

0 Likes
6
784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:29 PM . Last Modified: ‎2024-04-09 01:12 AM

Netbotz not always sending a proper attachment

We have all our Netbotz set to e-mail us with attached .avi files from the camera pods when a motion alert is triggered. This morning we had a large number of alerts from a couple of cameras and I noticed that not all of the alerts were being sent with attachments, and some of the attachments were .avi files with 181 bytes that were actually text files with the message "Output file write error --- out of disk space?"

The confusing thing is that every few minutes a proper attachment was sent, so even if the Netbotz space was full, it appears to have been deleting old files to make space for the new ones. 

Any assistance would be appreciated.

 

(CID:105462561)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:29 PM . Last Modified: ‎2024-04-09 01:12 AM

0 Likes
4
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:29 PM . Last Modified: ‎2024-04-09 01:12 AM

Hi Dominic,

 

The message alone doesn't really tell the full tale of what happened. There could indeed be an issue with disk space and the amount of data the NetBotz appliance is trying to both store and send out. The NetBotz appliance (both version 2 and version 3) will store up to 24 hours of information by default but based on how much new data it receives, it could delete some data that is less than 24 hours old in lieu of new data. That being said, I don't know that I have ever seen the appliance actually send that message in place of an actual image. Is it at all possible that this message was sent from the e-mail server? Is the NetBotz appliance set up to use external storage and perhaps it was unable to reach that storage?

If you have 4 cameras connected to a NetBotz appliance, if you're running a high frame rate, high resolution, and you are monitoring an active environment, you are much more likely to run into issues with the amount of resources used than if you are running at lower configurations and monitoring an environment off hours. If this is happening on a regular basis, I would definitely suggest changing your capture parameters to lower resolutions and / or frame rates. NetBotz are designed for environments where there should really be no motion and the motion alert is the exception.

 

Steve

(CID:105462564)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

In response to DCIM_Support
0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

Thanks for the reply. The Netbotz don't have external storage. A light was flashing in the data center, causing the Netbotz to send us an alert every minute or so.

If I Google the exact error message (together with a file of 0 bytes) I get a bunch of references to libjpeg errors - I don't know if that has any relevance to how the Netbotz operate. I can see all the clips in Data Center Expert, so it appears the camera is recording everything, but the appliance is unable to attach the .avi file to the e-mail.

(CID:105462571)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

In response to DCIM_Support
0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

Hi Dominic, You mentioned also that the attachments did come in on later e-mails. Since it's sending via e-mail and sending to (1? 2?) DCE server, it's doing 2x the work as well. It's sending the image via e-mail and sending it as an alert to DCE. I can check with engineering to see if they'e seen this before but I have not. I've asked around as well. What bot and what fw are you running? How many camera? How many other sensors and how many sensors were alerting total? How many e-mail addresses is the appliance sending to? Again, can you replicate this or was it a one time thing? Steve.

(CID:105462600)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

In response to DCIM_Support
0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

Steve, It's a Netbotz 355 wall appliance running v4_5_0_20150518_1808. There's only one DCE server, the camera is built-in, and that was the only sensor that was alerting at the time. We have two alert profiles that run concurrently, one to send to e-mail and text (seven addresses in total), and the other to send the alert to our FTP server. Going back through the history, today was the first time we received 0 byte files from this Netbotz. That said, the Netbotz used to only send images but since last Friday it's been configured to send avi files.

(CID:105462607)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

In response to DCIM_Support
0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2024-04-09 01:12 AM

Hi Dominic, So not too many alerts but you are sending images to 9 different destinations. DCE did get the alert you said. Did the FTP server also get the alert? Did all 7 e-mail recipients all receive this same message.... text files with the message "Output file write error --- out of disk space?" You mentioned that some got through but I wasn't clear if some alerts sent properly and other alerts did not or if some addresses were sent to properly and others were not. If the latter, is there anything different about the destinations? What is your frame rate? What is your resolution? How many images are being sent per alert? Can you replicate this? Steve

(CID:105462616)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2023-10-31 11:26 PM

0 Likes
0
785
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 11:30 PM . Last Modified: ‎2023-10-31 11:26 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of