Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:47 AM . Last Modified: 2024-04-09 12:49 AM
Hi all ,
I used Netbotz 570 to monitor Uniflair SDCV0400A by SNMP , it can connect but had no data ,
pls see the screenshot , does our netbotz not support this model ? Thanks .
Best Regards
(CID:105467918)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:47 AM . Last Modified: 2024-04-09 12:49 AM
Billy,
You'll need the DDF file to get sensors data to be shown. Now the tricky part is, this is Netbotz, I am not sure multivendor still creates/updates DDF file for Netbotz.
In the mean time, you can manually add a few OIDs under Netbotz's supplemental OIDs to get some sensor reading data. Get a copy of the Uniflair/pcoweb's MIB file from your local cooling expert.
Also, do take note on the minimum SNMP polling time for Netbotz is only 5 minutes.
Hope this helped.
Regards,
Chris
(CID:105467925)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:47 AM . Last Modified: 2024-04-09 12:49 AM
Billy,
You'll need the DDF file to get sensors data to be shown. Now the tricky part is, this is Netbotz, I am not sure multivendor still creates/updates DDF file for Netbotz.
In the mean time, you can manually add a few OIDs under Netbotz's supplemental OIDs to get some sensor reading data. Get a copy of the Uniflair/pcoweb's MIB file from your local cooling expert.
Also, do take note on the minimum SNMP polling time for Netbotz is only 5 minutes.
Hope this helped.
Regards,
Chris
(CID:105467925)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:47 AM . Last Modified: 2024-04-09 12:49 AM
Hi Christopherus , Thank you for kindly advise , I also concern if the DDF can support Netbotz , Anyway ,I'll check the multi support ,thank you . Best Regards
(CID:105467926)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:47 AM . Last Modified: 2024-04-09 12:49 AM
Hi Chris, Chu, No, Multivendor is not creating DDFs for NetBotz at this time and supplemental OIDs are the only alternative without an existing DDF. Please note we will only accurately work with numeric sensors and not text when using this option. You may want to look into the free 5 node DCE VM server. Steve
(CID:105467982)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 12:47 AM . Last Modified: 2023-10-31 11:25 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.