Netbotz 450 going offline "connectivity error"

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz 450 going offline "connectivity error"
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:46 PM . Last Modified: ‎2024-04-09 02:41 AM

0 Likes
4
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:46 PM . Last Modified: ‎2024-04-09 02:41 AM

Netbotz 450 going offline "connectivity error"

We had newly installed Netbotz Rack monitor 450 and we have leak sensor cable connected to it.

Even not required we had connected the A link port of 450 to A link of Netbotz 200 in the same network. The 450 detected the unit but the all sensors were showing in unplugged status. After a day the cable from Alink port of 450 was disconnected and after that the 450 unit went Offline and I am not even able to access the console port.

There is message in StruxureWare Expert saying unit is offline due to connectivity error.

But as soon as I connect the Alink port of 450 back, the unit will be online. please advise why this is happening and a procedure for factory reset of 450.

 

(CID:103585866)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:46 PM . Last Modified: ‎2024-04-09 02:41 AM

0 Likes
1
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:46 PM . Last Modified: ‎2024-04-09 02:41 AM

Shemilusman,

The NetBotz 450 and NetBotz 200 are two stand-alone appliances and should not be connected with an A-link cable. The A-link cable outputs power, but only for sensors and sensor pods.

When the two NetBotz systems are not connected, are there any lights lit on the NetBotz 450? If there are not, ensure that the Netbotz 450 is connected to a known working power source via the AC line inlet power port.

If the appliance is powered on, are you able to ping it and log in using the web browser / advanced view application?

Best Regards,
Cory

(CID:103585877)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:46 PM . Last Modified: ‎2024-04-09 02:41 AM

In response to DCIM_Support
0 Likes
0
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:46 PM . Last Modified: ‎2024-04-09 02:41 AM

Hi Cory, I did the mistake of connecting the Netbotz 200 and 450 A links ports. But now I did disconnect the A-link cable and performed "Re-flash firmware using TFTP procedure" using console access and the device is working fine. Regards Shemil

(CID:103586154)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:47 PM . Last Modified: ‎2024-04-09 02:41 AM

0 Likes
0
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:47 PM . Last Modified: ‎2024-04-09 02:41 AM

Hi All,

I disconnected the A-link cable between Netbotz 450 & 200 and performed "Re-flash firmware using TFTP procedure" using console access and the Netbotz 450 is working fine.

Regards

Shemil

(CID:103586155)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:47 PM . Last Modified: ‎2023-10-31 11:24 PM

0 Likes
0
655
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:47 PM . Last Modified: ‎2023-10-31 11:24 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of