Hello,
Would it be possible that by using the NBES0304 dry contact cable in the Netbotz 450/550/570 along with several Ap9619 SMART UPS NMC I could get an SMS when powere is out or when the UPS has a fault ?
I've read that the Ap9619 has a configurable relay that is able to close or open on event basis. This led me to think that I could hook up a dry contact cable from Netbotz appliances to a NMC card relay and get useful information via SMS (and via e-mail of course) in the event of a power outage or something similar.
Thanks,
Petru
(CID:137726201)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:31 PM . Last Modified: β2024-04-03 11:24 PM
Hi Petru,
That would likely work but the recommended solution for this requirement would be to use a NetBotz 570 with the 5-node monitoring license (NBWN0006) to discover the NMC, and then configure an alert based on its status.
Regards,
Steven
(CID:137726403)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:31 PM . Last Modified: β2024-04-03 11:24 PM
Dear petru bunea,
I think if a ethernet network is available for your UPS, then itβs better to just use its NMC without even connecting and buying additional licenses for the NetBotz-4.x appliance.
Indeed, in the above mentioned NMC there is a complete set for event notification, including by e-mail. And if you want to be notify via SMS, then you can use public email to SMS gateways of mobile operators in your country.
With respect.
(CID:137726268)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:32 PM . Last Modified: β2024-04-03 11:24 PM
Dear petru bunea,
Please tell us if you could solve your question or not?
With respect.
(CID:137729847)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-05 03:32 PM . Last Modified: β2023-10-22 03:19 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.