Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!
EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:34 PM . Last Modified: 2024-04-05 02:35 AM
Hi Team,
Question from existing customer:
"...we are wanting to setup/configure 2 person card access to the APC racks i.e. both pers will need to swipe their RFID card before the door will unlock (not just 1)..."
As far as I know currently this is not supported...happy to be told it is 🙂
Any plans this will be supported (already on a feature request list) and if not can this be please added to feature requests.
(CID:128761670)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:34 PM . Last Modified: 2024-04-05 02:35 AM
That's in 570 isn' it?
Feature request +1.... 😀
(CID:128761894)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:34 PM . Last Modified: 2024-04-05 02:35 AM
Hi Lukast,
Looking at rack access POD170 (NBPD0171)
This access POD is compatible with the 455 & 570 (NBWL0455 & NBRK0570)
A maximum of 200 cards is supported on NetBotz Rack Monitor 550/570 and Room Monitor 455 using the Rack Access Pod 170. Authorization card swipes.
There are two levels of authorization for cards in the Rack Access System. A Level One card does not require authorization from another card to access assigned doors. A Level Two card has the “Requires authorization card swipe” checkbox selected. When a Level Two card is swiped, it must be followed by a swipe from a Level One card before the Auto-Lock timer expires in order to access the door. Both cards must have valid access to the door in order for access to be granted. If the Auto Lock timer expires without the Level One swipe, the Level Two card must be swiped again before the authorization swipe can occur.
I don’t see this option for the NetBotz 250.
Regards, Rich...
(CID:129408767)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:34 PM . Last Modified: 2023-10-22 03:16 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.