Netbotz 200 can not auto re-connect by DCE after power shutdown

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz 200 can not auto re-connect by DCE after power shutdown
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:00 PM . Last Modified: ‎2024-04-09 02:57 AM

0 Likes
3
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:00 PM . Last Modified: ‎2024-04-09 02:57 AM

Netbotz 200 can not auto re-connect by DCE after power shutdown

Hi All ,

 

Our customer used DCE monitor Netbotz 200 , due to they have annual maintenance and shutdown the

power in the IT room ,  our netbotz seems be failure and can't auto re-connect by DCE after power return.

It's need on site to use console to reboot it , then DCE can reach netbotz .

Does netbotz 200 have no auto re-start function ? This issue also happen on two different site .  

Pls kindly advise ,many thanks .

Best Regards

(CID:103584049)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:00 PM . Last Modified: ‎2024-04-09 02:57 AM

0 Likes
1
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:00 PM . Last Modified: ‎2024-04-09 02:57 AM

Hi Chu,

 

If the 200 was simply powered off and back on again, DCE should be able to detect it. I would suggest some troubleshooting. An easy test is to simply disconnect the 200 from power and reconnect it. Once the 200 is up and DCE scans it, DCE should show it back on line. If not, try to connect to the web page of the 200. If you can get there, try connecting to the 200 using SNMP as this is the protocol DCE uses for it's communications. If you can get to the 200 via SNMP but DCE can not poll it, right click the device in DCE and choose "request device scan". If it comes back on line, then it likely did not poll the device yet.

 

If this troubleshooting does not show the same lost comm behavior, perhaps it is something specific to the network or maybe the sequence in which the devices returned to an operational state. It may be more difficult to troubleshoot this. If routers and switches were also taken down during this maintenance period, the proper troubleshooting for this issue would be to replicate the power down and power up of these devices in the same sequence. I'm guessing however that this might not be a desirable option as everything would lose comm for at least a short period of time.


Steve

(CID:103584071)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:00 PM . Last Modified: ‎2024-04-09 02:57 AM

In response to DCIM_Support
0 Likes
0
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:00 PM . Last Modified: ‎2024-04-09 02:57 AM

Hi Steve , Thanks for your kindly advise , I will test the SNMP and get back to you . Many thanks . Best Regards

(CID:103584152)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 04:01 PM . Last Modified: ‎2023-10-31 11:23 PM

0 Likes
0
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 04:01 PM . Last Modified: ‎2023-10-31 11:23 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of