NetBotz POD device ID 88

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NetBotz POD device ID 88
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
GaborNovak
Lieutenant JG GaborNovak
Lieutenant JG

Posted: ‎2020-09-30 01:26 AM

0 Likes
8
3531
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-30 01:26 AM

NetBotz POD device ID 88

 

I have setup a new NetBotz 750 system, a few sensor POD is showing device ID 88.

I have seen this number when the system is starting up, or when it updates the firmware.

The NetBotz is showing the following alarms:

  • Disconnected Pod: Appliance
  • Disconnected Pod: Appliance Rack Access

 

NetBotz alarm.png

 

I have noticed that I have to sensor pod with ID 1.

 

What can be the problem?

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
GaborNovak
Lieutenant JG GaborNovak
Lieutenant JG

Posted: ‎2020-09-30 08:42 AM

0 Likes
7
3505
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-30 08:42 AM

The NetBotz 750 A-link communication is built up as the picture shows.

 

NetBotz 750 A-link connection.png

 

The NetBotz 750 has two A-link connection when the first time I have started the systems I have connected one by one the sensor pods. The sensor pods received the ID numbers. POD 1- POD 6
I have started to connect the A-link cable to the secund A-link port on the NetBotz 750. The POD is getting the ID 1 another ID 88 and then ID 88.

The NetBotz 750 shows error message which was attached in my previous post.

 

 

This way can handle the NetBotz 750 the A-link cable and the sensor pods?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Mike-Sutton
Lieutenant Mike-Sutton
Lieutenant

Posted: ‎2020-10-01 01:38 AM

In response to GaborNovak
0 Likes
6
3478
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-01 01:38 AM

Hi Gabor,

 

Have you tried using 24v power supplies on every 4th sensor pod as you might have overloaded the A Link Bus ?? This has solved promblems like this for me before.

Try connecting them to only 1 port on the 750 and see if this works as you can cascade up to 12 sensor pod 150's

 

Regards,

 

Mike

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

GaborNovak
Lieutenant JG GaborNovak
Lieutenant JG

Posted: ‎2020-10-01 09:53 AM

In response to Mike-Sutton
0 Likes
5
3450
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-01 09:53 AM

Hi Mike,

I have started with the pod number 1 and then followed by pod 2 end so on. I extend with 24v power supply every 3th sensor pod, which I connect after I have connected the A-link cable.
Everything was working well. When I have connected the pod 6 this pod has got the ID number 1. I have tried to work with the second A-link line which was started from the other A-link port from the NetBotz 750. In this line the first pod was getting the ID 1. In this point this was the third pod with ID number 1. If you look my previously attached picture the pod 1 ID has pod 1, pod 6, pod 7. Pod 8-10 is getting the 88 ID number.
The Netbotz 750 shows alarm (see my starting post)

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

GaborNovak
Lieutenant JG GaborNovak
Lieutenant JG

Posted: ‎2020-10-05 12:23 PM

In response to GaborNovak
0 Likes
4
3428
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-05 12:23 PM

I have reset the device and configured the IP parameters. The NetBotz has still alarms. I have updated the firmware, now it runs on 5.2.3 version.

It doesn’t recognize the sensor pod. I have deleted them before the reset.

Question, when I have deleted a sensor pod than can the NetBotz 750 recognize them again?

 

alarm.PNGoverview.PNG

 

What can be the problem with this NetBotz 750 system?

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2020-10-06 12:26 AM

In response to GaborNovak
0 Likes
0
3417
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-10-06 12:26 AM

Hi Gabor,

 

It might be no harm to log a ticket with your local support team, this might require some bus level debugging.

 

- Gavan

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-08 09:36 AM

In response to GaborNovak
0 Likes
2
2941
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-08 09:36 AM

Hello @GaborNovak ,

 

I did the exact same procedure as you did on my netbotz rack monitor 550, and now my internal pod has no readings (temperature, humidity and dew point).

 

Did you ever get this problem solved?

 

Can you please share how should I proceed?

 

Thanks in advance!

 

Best regards

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

GaborNovak
Lieutenant JG GaborNovak
Lieutenant JG

Posted: ‎2021-04-09 07:06 AM

In response to Anonymous user
0 Likes
1
2923
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-09 07:06 AM

@Anonymous user 

 

I had this issue with NetBotz 750 system.

Which NetBotz system are you using?

NetBotz 750 or NetBotz 550?

 

If you are using other NetBotz device it is recommend to start a new topic with the question. In that way we don’t mix the topic.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-04-09 07:53 AM

In response to GaborNovak
0 Likes
0
2918
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-04-09 07:53 AM

Hello @GaborNovak ,

 

Thanks for your answer!

 

My device is a Netbotz 550.

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.