NMS Integration SNMP Trap vs an Alert SNMP Trap

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • NMS Integration SNMP Trap vs an Alert SNMP Trap
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT Forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

0 Likes
4
1119
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

NMS Integration SNMP Trap vs an Alert SNMP Trap

We are looking into sending traps from DCE to HPe Operations Manager environment. Can someone list the positives and/or negatives of using these two trap sending methods? What's the difference between the two?

(CID:105469726)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

0 Likes
0
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

Hi Dan,

 

If you search k-base (here) for this k-base, FA236815, it outlines some of the differences so you can see the data itself. As for which is better, that's a little tougher. I believe if you'd dealing with the pre-configured alerts such as with APC devices, you will get equal amounts of information. You may have a preference to how it is presented and again FA236815 may help you there, If you're using a lot of manually created thresholds, I'm not sure that as much information will be sent using the alarm action trap. 

Pretty much any alarm can be configured to send either trap. The NMS integration should send any alert you see in DCE as long as it is set to the proper severity level. The SNMP alarm action needs to be added to a notification policy or multiple notification policies should you have your server configured that way. You then need to associate that notification policy to the manually created thresholds in Alarm Configuration/ Threshold Alarm Configurations or to a device for the pre-configured alarms in the Alarm Configuration/Device Alarm Configurations section.

 

Steve

(CID:105469730)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

0 Likes
1
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

Hi, 

we use AZETI Sonarplex as NMS, to pull traps directly from Netbotz appliances however only one Netbotz 455 worked(ping OK and MIB scan successful and we are getting values in AZETI) however Ping is ok for the rest of them but we can not read the MIB or configure any OID.

 

Would you have an idea what could be the problem

 

Thanks

(CID:106207904)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

In response to DCIM_Support
0 Likes
0
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2024-04-09 12:36 AM

Hi Amine, Is this related to the initial question in some way? If not, you may want to post a separate issue for future questions. If the NetBotz is on the network, make sure you've logged into the appliance and verified SNMP is running, verify you're using the correct community names etc, There cal also be issues with networks blocking SNMP so you may want to try connecting with a crossover cable to remove the network as a possible issue. You also mentioned you "can not read the MIB or configure any OID." Reading is again something to troubleshoot such as on the network. Configuring an OID is usually referred to as a write. NetBotz OIDs can not be written. Another thing to consider is the version NetBotz appliance, the 3xx, 4xx, and 5xx series are tru NetBotz and use the NetBotz Mib and the 1.3.6.1.4.1.5528 OID. If you have NetBotz Rack access or the NetBotz 200, that would use the APC Powernet Mib 1.3.6.1.4.1.318. Steve

(CID:106207905)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2023-10-31 11:27 PM

0 Likes
0
1120
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 01:27 AM . Last Modified: ‎2023-10-31 11:27 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore