My client has been troubled by an issue recently. His camera cannot reliably detect people passing by the door. The distance from the camera to the door is approximately 15 meters. He wants to know the focal length of the NBPD0160 camera. What is the recommended optimal monitoring distance range in meters?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-01 04:03 PM
Hi @fredteng,
Camera Pod 165's should be connected to a NetBotz 750/755 and are dependent on the number of pixels changing to detect if there is motion or not. As long as within the camera image you can see the section that you wish to monitor you should be able to make some adjustments to sensitivity to capture at that distance.
You can find the details of the sensitivity setting within the "Configure the Camera Pod Settings" section of the NetBotz 5.X User Guide: https://download.schneider-electric.com/files?p_Doc_Ref=990-5934_EN&p_enDocType=User+guide&p_File_Na...
Kind Regards,
Cory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-05-01 04:03 PM
Hi @fredteng,
Camera Pod 165's should be connected to a NetBotz 750/755 and are dependent on the number of pixels changing to detect if there is motion or not. As long as within the camera image you can see the section that you wish to monitor you should be able to make some adjustments to sensitivity to capture at that distance.
You can find the details of the sensitivity setting within the "Configure the Camera Pod Settings" section of the NetBotz 5.X User Guide: https://download.schneider-electric.com/files?p_Doc_Ref=990-5934_EN&p_enDocType=User+guide&p_File_Na...
Kind Regards,
Cory